    Originally posted by flangehead
    ....if system has a txv hold bulb in hand and watch your gauges, if gauges don't respond, replace txv. ...
    Good advice.....but how does one watch the guages when the TXV bulb is at the evaporator, but the guages are outside (at the condensor). Must be a 2 person type of test I suppose, a real good one though...thanks!


  2. #15
    Join Date
    Jun 2003
    Location
    Jacksonville, FL.
    Posts
    4,313
    I bet it was the TXV all along.

  3. #16
    Join Date
    May 2005
    Posts
    13
    Was compressor a scroll, maybe I missed that, There are problems with scrolls run for a period on a flat leaking system. They can give your exact symptoms.
    Clean up the system by pulling charge, new F/D on the liq. line and a deep vac.
    If it is a scroll and you notice a strong acrid smell that follows you around for several days; problem will probably reoccur.

    of course, you gotta fix the leak first. LOL

  4. #17
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    67,875
    Originally posted by latent

    If it is a scroll and you notice a strong acrid smell that follows you around for several days;

    It means you need better personal hygiene.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  5. #18
    Join Date
    Mar 2005
    Location
    Suppy NC
    Posts
    4,513
    hvac gut goes to the doctor with a broken leg
    doc says instead of fixing your leg. i will just give you a new one. your an hvac guy so its ok right

  6. #19
    Join Date
    May 2005
    Location
    lawn guyland, ny
    Posts
    27
    twenty bucks says unit will have same problems as old one. if you don't take the time to find out what killed the previous compressor, you are destined to kill this one. ditto on the symptoms; air, water, txv, clogged/frozen orifice, kinked line,clogged drier. did anyone bother to flush system and install replaceable core suction line driers after first burnout? is all that good sludge and winding bits still in the system? eff him, he's a doctor right? wow.

  7. #20
    Join Date
    May 2005
    Posts
    13
    Originally posted by beenthere
    Originally posted by latent

    If it is a scroll and you notice a strong acrid smell that follows you around for several days;

    It means you need better personal hygiene.
    Thanks, I was wondering why my calls had fallen off recently

Page 2 of 2 FirstFirst 12

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event