Results 1 to 6 of 6
  1. #1
    Join Date
    Apr 2005
    Posts
    59
    Can the condenser unit of the heat pump system be installed under the deck's stairs or does it have to installed somewhere more open?

  2. #2
    Join Date
    Sep 2001
    Location
    Vancouver Canada
    Posts
    996
    check the installation manual, it will give all recommended clearences. I would think if the stairs have open runners it would be a lot better than if they were closed in.

  3. #3
    Join Date
    Aug 2002
    Location
    Office and warehouse in both Crystal River & New Port Richey ,FL
    Posts
    18,836
    If fan is top discharge,usually four feet unobstructed above is required.

  4. #4
    Join Date
    Apr 2005
    Location
    NE PA
    Posts
    698
    Heat pumps need a large supply of air to maintain efficiency, escpecially in the cold parts of winter and the high heat of summer. Putting the compressor unit in an area wher the unit is likely to regurgitate the air will cause a significant drop in efficiency and capacity.

    paul

  5. #5
    Join Date
    Jan 2005
    Posts
    340
    Originally posted by dash
    If fan is top discharge,usually four feet unobstructed above is required.
    Five feet for Trane.

  6. #6
    Join Date
    Apr 2005
    Posts
    59
    Thanks!