    Confused

    Today I noticed that some just installed AC ducting in attic is on the floor of our soon to be finished attic. The other ducts have been run overhead, i.e will be out of the way, above the ceiling, when the attic is finished. These ducts on the floor will cool my office on the 2nd floor of our under-construction (modular)house.


    The office will have its own zone, remainder of the upstairs (4 bedrooms, 2 bathrooms)on 2nd zone.

    Why would they run those ducts on the floor when they know we intend to finish the space? Could they have run them up (what will be) above the ceiling?

    Our builder's project manager prefers that we do not talk directly to the subcontractors so I do not know if I will be able to ask the HVAC contactor this question before I talk to the builder in a few days. The one meeting we had with the HVAC contractor was great.

    Air handler in the attic is Carrier model FK4DNB006000AAAA. I think we are getting a Carrier Performance 13, which with the more expensive 3 speed air handler will give us a SEER of 15. Opted for a 4 ton unit so that we can duct and cool the attic when we finish it.

    [Edited by whynot on 05-30-2005 at 11:08 AM]

  2. #2
    Join Date
    Jul 2004
    Location
    midwest
    Posts
    2,868
    Looks to me like you are going to get a window seat the length of that wall. The flex system looks very poorly installed with alot of airflow problems. When you put a new roof on and they use longer nails what do you think will happen to that flex.

  3. #3
    Join Date
    Feb 2004
    Location
    cocoa fl
    Posts
    143
    sorry if this is rude but that looks terrible. total lack of quality.did they have monkeys do the duct work ?

  4. #4
    Join Date
    May 2005
    Location
    Mississippi
    Posts
    102
    that flex looks to be a larger diameter than the rafter is deep. will get crushed somewhat when the ceiling goes up. Its probalby already full of holes from either nails or staples anyway.

    Also, looks like somebody likes to run flex instead of spend a little time and run rigid.

    I am not trying to be critical of someones work, but I would call the construction manager and "86" this HVAC Contractor right now; no pride in work that i can see and appears destined for problems.

    By the way, thats a 5 ton Fan Coil unit in the attic.

    my $.05 worth.

    Regards



    [Edited by biscuitnt on 05-30-2005 at 12:13 AM]

  5. #5
    Join Date
    Nov 2003
    Posts
    125

    Arrow

    Maybe you'd better tell them to take that duct out and put you a window unit in.

    Or tell the project manager to get with the HVAC contractor and figure out how to get from there to there without taking up your floor space.

  6. #6
    Join Date
    Nov 2004
    Location
    SW FL
    Posts
    5,987

    Monkeys Definitely !

    Originally posted by centralflinstaller
    sorry if this is rude but that looks terrible. total lack of quality. did they have monkeys do the duct work ?
    INSANITY Redefined ! !!

    Discuss Ductless mini-split (i.e. Mitsubishi Mr. Slim or Sanyo) and removing ALL the pictured duct with G.C.

    http://www.mrslim.com/Products/Categ...ctCategoryID=7

    If he does not listen and ACT to meet ALL your expectations, It is time STOP ALL WORK and call your lawyer.

    Much Better to STOP NOW
    than proceed down the path to Hell.

    It appears that ... Most 4 year-olds KNOW Better! !!

    Professionally speaking, of course.
    Designer Dan
    It's Not Rocket Science, But It is SCIENCE with "Some Art". ___ ___ K EEP I T S IMPLE & S INCERE

    Define the Building Envelope and Perform a Detailed Load Calc: It's ALL About Windows and Make-up Air Requirements. Know Your Equipment Capabilities

  7. #7
    Join Date
    Feb 2003
    Location
    Huntsville,AL
    Posts
    4,125
    do the house drawings state the attic is to be finished?
    does the gen contractor know this?
    what is your contractual agreement?

  8. #8
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    66,755
    Look at the way the metal brakets are colasping the flex, now picture what the drywall will do.

    Your air system needs to be redesigned NOW!

    Get with your GC ASAP, don't delay.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  9. #9
    Join Date
    Feb 2004
    Location
    chicago suburbs
    Posts
    4,422
    yet ANOTHER wonderful flex system. never ceases to amaze me. screw the homeowner.... do it as cheap as possible with the cheapest labor available. who cares if it works. f the customer. HOOORAY for me. we got paid.

    sorry to say.... stop it now and call your attorney. it's probably gonna get ugly.
    FILL OUT YOUR PROFILE!!

  10. #10
    Join Date
    May 2005
    Location
    Mississippi
    Posts
    102
    Just to extend on my earlier reply, As others have stated, you need to stop work now.

    You stated the remainder of the upstairs would consist of 4 bedrooms and two baths, I must assume you will have a substantial investment in this home; As a result , you have to get with you GC and demand a certain degree of quality.

    If he is going the cheap route to this degree on your "comfort systems" , I have to wonder about the rest.

    Just my advice that you really need to have a "sit-down" with him immediately.

    Regards and good luck,


    David Graves

  11. #11
    Join Date
    Oct 2001
    Location
    Waterford Michigan
    Posts
    2,668
    A good example of a poorly thought-out system for a two story modular home, but not unusual as most modular homes leave allot to be desired from the manufacture when it comes to second story heat and cool.

  12. #12
    Join Date
    Feb 2004
    Location
    chicago suburbs
    Posts
    4,422
    print this thread and show it to the GC. this is what people in the trade think of the work going on here. it's deplorable. if he has any scruples he will address your problems. good luck..you're gonna need it.
    FILL OUT YOUR PROFILE!!

  13. #13
    Join Date
    Nov 2004
    Location
    Atlanta, Ga. burbs
    Posts
    281

    A Homeowners response

    The people that do HVAC for a living summed it up in short order. Poor poor quality, craftsmanship, and workmanship. You will have MANY MANY problems. The time to do something is NOW ASAP. My advice is to ADDRESS it and don't let it slide. Raise "H" if the request to make it right does not happen. I would also QUESTION the rest of the job if this part was so sadly installed!! I would have a long talk with the company who sent the monkeys out/talk to the local inspectors/hire someone to oversee the job/and/or fire as appropriate. Hire a lawyer, watch out for mechanics liens but stand up.

    How do I know? My cape cod has a bonus room off the garage that looks similiar to what your pictures depict. Currently in Georgia BUILDERS are not licensed. HVAC, electrical, and plumbers have to be but not builders. My builder tried to take short cuts on me. I admit some got past us since we "trusted" the dirt bag. It took years and years of re-doing what this )expletive deleted( slob allowed to happen on our house. This included the HVAC system. Twice the work, twice the pain, and triple the cost of not doing it right the first time!! Besides the fact we could not use our home in comfort or even peace of mind.

    So, get it fixed, get it right, and do it your satisfaction. You are very lucky in this day and age where you can post to a board where professionals are willing to give up their time to try and make the industry they are in better for people like us.

    Best of luck and you WILL PREVAIL if you move on this!!

Page 1 of 3 123 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event