Page 2 of 2 FirstFirst 12
Results 14 to 16 of 16
  1. #14
    Join Date
    Jan 2004
    Location
    PA
    Posts
    74,513
    Post Likes
    Originally posted by acmanko
    Originally posted by beenthere
    I have a pontiac firebird, with 89 octane, at 90 miles an hour, can anybody tell me what it should be taching.



    no more then 3500rpm any more and the old pos will fall apart.
    LOL...

    At 3500rpm, it'd be doing over a hundred.

    But it is a POS, of course, its get me where i want to go.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  2. #15
    Join Date
    May 2005
    Posts
    4
    Post Likes
    Good catch, long day, I meant cooling mode.

    Mike

  3. #16
    Join Date
    Mar 2004
    Location
    Niceville,Fl.
    Posts
    65
    Post Likes
    The pressure on the highsideshould be about 225 to 300. If the line temperature is close to the outside temp. your probaly overcharged. Look at the pressure chart or you gages and subtract the line temperature from the actual temp that will give you the subcool. If you have a high efficentcy system then it should be around 12-15 degrees. This is the only way to charge a TXV system properly. For a cappallary tube or orafice system superheat is the way and just do the same with the temerature and pressure on that side of the system.
    Too Old to be doing this

Page 2 of 2 FirstFirst 12

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Related Forums

Plumbing Talks | Contractor MagazineThe place where Electrical professionals meet.