    Another frozen walk in...

    What do you guys think? Equipment info below:
    (I think it was Bohn equipment)
    Evap - ba82p-a-sia-tsm2a1/050205276
    Cond - beha008h2-hs2a-b/050207420
    No outdoor fan cycling control. No defrost timer.

    Arrived after 1st call, different tech (evap frozen up...bottom 1/2 of coil)
    On this 2nd call found same prblem. Bottom 1/3 of coil frozen. Drain line clear.
    THawed out ENTIRE coil. No ice left except on the sides on the return bends. FIred up back up...Superheat after 15 minutes of run time @30 deg F.
    Adjusted valve out 1 full turn. Super heat after 15 minutes down to 18 deg F...
    Went down and backed out valve 1/2 turn...superheat back up to 27-30deg F, but every 5 minutes the superheat would drop like a rock down to 13 degrees then right back up in the upper 20's. Let run for 15 min, no change. ....now frustrated. Backed valve out 2 turns and superheat immediately dropped to around 10-13 deg F. Let run for 30 minutes and superheat never changed from that. (This was all done with box running around design temp of 32 deg F.

    Now, i noticed after all this that a very very light frost was forming on the bottom 1/3 of the coil on the return side...all the distributor caps are frosted. (Box down around 30-32 now and about satisfied).
    I think, and hope, that ive solved the icing issue by adjusting the TXV (although the TXV may on the way out and need to be replaced soon).
    Current outdoor ambient is at 65 deg F.
    R-22 system.
    Low side psi 40.
    High side psi 190 ( if i remember correctly).
    Sight glass full of liquid.

    Do you think I might have nailed it with the TXV adj. or is that bottom 1/3 frosting suspicious? If so...any ideas?

    THanks guys...

  2. #2
    Join Date
    May 2010
    Posts
    1,296
    Post Likes
    Condensor fans operating at correct amperages? Low charge? Restricted TXV or Filter drier, faulty thermostat? I am assuming bad TXV

  3. #3
    Join Date
    Feb 2007
    Location
    Northern NJ
    Posts
    829
    Post Likes
    I would drop the superheat a little more, try around eight degrees. Does this unit have a headmaster?

    I am still trying to fathom how you are running this box to 32 degrees with nothing but off cycle defrost- maybe the problem is that the bottom of the coil can't get warm enough on the off cycle to clear the frost.

    Is this a pumpdown system, or does it drop out?

  4. #4
    Join Date
    May 2010
    Posts
    1,296
    Post Likes
    Oh... Didn't read no defrost timer. Interesting

  5. #5
    Join Date
    Feb 2011
    Posts
    3
    Post Likes

    Angry another frozen walk-in

    i have had same problem before replaced t-stat to start. after that was still getting same thing froze 1/3 to 1/2 way up. replaced txv havent been back except for normal service. problem happened about 2 years ago. owner called today and walk-in froze again. have to go tommrow and ckeck it.

  6. #6
    Join Date
    Nov 2007
    Location
    NC
    Posts
    145
    Post Likes
    Thread Starter
    Quote Originally Posted by tjc76 View Post
    I would drop the superheat a little more, try around eight degrees. Does this unit have a headmaster?

    I am still trying to fathom how you are running this box to 32 degrees with nothing but off cycle defrost- maybe the problem is that the bottom of the coil can't get warm enough on the off cycle to clear the frost.

    Is this a pumpdown system, or does it drop out?
    Yea, thought that was kind of odd also...but...box has been running for 6 years like that.
    Pump down system.

  7. #7
    Join Date
    Jan 2008
    Location
    michigan
    Posts
    1,187
    Post Likes
    How often are they in and out of this box?

  8. #8
    Join Date
    Aug 2006
    Location
    st.petersburg,fl
    Posts
    846
    Post Likes

    Lightbulb

    Theres more to this story...

    Also sounds like you are oil logging in the evap need to force it back into condenser and you also need some kind of low ambient controls on this unit and absolutly need to be on pumpdown set up with defrost timer...
    Isn't sanity just a one-trick pony anyway? I mean, all you get is that one trick, rational thinking, but when you're good and crazy, well, the sky's the limit!

  9. #9
    Join Date
    Aug 2006
    Location
    st.petersburg,fl
    Posts
    846
    Post Likes

    Lightbulb

    Also depending what is kept in this box , I'd get the box close to temp and shoot for 10* sh at evap and make sure you are no less than 20* SH and NO more than 40* SH at condenser....

    Hope this helps...
    Isn't sanity just a one-trick pony anyway? I mean, all you get is that one trick, rational thinking, but when you're good and crazy, well, the sky's the limit!

  10. #10
    Join Date
    Feb 2011
    Posts
    3
    Post Likes
    Quote Originally Posted by monkeyman#1 View Post
    How often are they in and out of this box?
    often i'm sure. and they tend to leave door open about 3 to 5 inches. they have curtin and told owner not for any reason let them leave door open. but i'm sure it happens.

  11. #11
    Join Date
    Nov 2007
    Location
    NC
    Posts
    145
    Post Likes
    Thread Starter
    Quote Originally Posted by skpkey9 View Post
    Theres more to this story...

    Also sounds like you are oil logging in the evap need to force it back into condenser and you also need some kind of low ambient controls on this unit and absolutly need to be on pumpdown set up with defrost timer...
    Why would i be oil logging in the evap?
    I agree that it may need a defrost control but it hasn't in 6 years....and they have had it at the same temp the whole time...

  12. #12
    Join Date
    Apr 2003
    Location
    New York
    Posts
    768
    Post Likes
    Quote Originally Posted by ZeroTolerance View Post
    Oh... Didn't read no defrost timer. Interesting
    hmm

  13. #13
    Join Date
    Aug 2006
    Location
    st.petersburg,fl
    Posts
    846
    Post Likes

    Lightbulb

    Easy low ambient, pressures fall low enough to where there not enough velocity to return oil causes lower few inches of coil to Ice up, same thing if the coil is iced up and its also unknown if there is a p- trap installed , also tell tale sign of oil logging is the lower portion of evap icing and not the rest if infiltration or door being left open top half of coil would be icing up and if it were a defrost issue the entire evap coil would be icing up...

    Hope this helps....
    Isn't sanity just a one-trick pony anyway? I mean, all you get is that one trick, rational thinking, but when you're good and crazy, well, the sky's the limit!

  14. #14
    Join Date
    Nov 2007
    Location
    NC
    Posts
    145
    Post Likes
    Thread Starter
    Good call skp.
    No oil trap installed.
    Cond. is on roof above evap.

    Why would oil logging in bottom of evap be the cause of frosting? WOuld it just ask as an insulator? Causing bottom of coil to be inefficient at picking up heat, causing coil to run cold.

  15. #15
    Join Date
    Feb 2006
    Location
    USA
    Posts
    4,381
    Post Likes
    ive never experienced oil logging .. that's interesting to know though because while reading OP I was thinking something more along the lines of it being in relation to the TEV .. like a partial restriction from a fouled up inlet screen or trash in the valve

  16. #16
    Join Date
    Nov 2007
    Location
    NC
    Posts
    145
    Post Likes
    Thread Starter
    Quote Originally Posted by hvac wiz 33 View Post
    ive never experienced oil logging .. that's interesting to know though because while reading OP I was thinking something more along the lines of it being in relation to the TEV .. like a partial restriction from a fouled up inlet screen or trash in the valve
    Now THAT is what i was hoping somebody would say. Thats what ive been thinking....

  17. #17
    Join Date
    Aug 2006
    Location
    st.petersburg,fl
    Posts
    846
    Post Likes
    sandpipertech - basically yes...


    hvac wiz 33 - that would cause a whole new and different set of issues...
    Isn't sanity just a one-trick pony anyway? I mean, all you get is that one trick, rational thinking, but when you're good and crazy, well, the sky's the limit!

  18. #18
    Join Date
    May 2010
    Posts
    1,296
    Post Likes
    Good to know skp. Didn't think of that and probably never would have :P

  19. #19
    Join Date
    Jan 2010
    Posts
    274
    Post Likes
    could it be unequal circuit loading due to a dirty evaporator making the bottom of the coil to get less airflow then the top

  20. #20
    Join Date
    Aug 2006
    Location
    st.petersburg,fl
    Posts
    846
    Post Likes

    Lightbulb

    Disable you condenser fans and heat up your TEV bulb to open valves and the higher pressures will force oil back into compressor, check levels on compresor sightglass if any to ensure you now don't have to much oil in system ( ie from compressor change out if any were done ) , if you do adjust accordingly. now that you have moved oil back where it belongs . Now its time to make the necessery repairs to prevent this from happening again...

    Hope this helps...
    Isn't sanity just a one-trick pony anyway? I mean, all you get is that one trick, rational thinking, but when you're good and crazy, well, the sky's the limit!

+ Reply to Thread
Page 1 of 2 12 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •