    I had a customer yell at me because his air conditioner will not come on when its below 12c (low ambient switch)

    He said whats the point of having an air conditioner then!

    Anyways I kinda wanna go rip out his low ambient and have him sign a waiver that theres no warranty!

    oh well thanks for listening


  2. #2
    Join Date
    Aug 2004
    Location
    North Richland Hills, Texas
    Posts
    15,103
    Post Likes
    Is it a commercial application? Lots of people and office equipment? He may need the air conditioning, even in very low ambient conditions.
    If its residential, is it a media room, or something else with very high internal heat gain?

    Give him a price for installing a low ambient head pressure control, evaperator defrost control, and wind breaks around the condensor. Some units may also require a hard start kit for low ambient operation, even with scroll compressors. Definatly install a crankcase heater if there isn't already one in place.
    RSES Certificate Member
    RSES-SWRA President

    You're not finished learning until you're dead!

  3. #3
    Join Date
    Apr 2003
    Location
    Calgary Alberta
    Posts
    77
    Post Likes
    Thread Starter
    Its residential


  4. #4
    Join Date
    Aug 2004
    Location
    North Richland Hills, Texas
    Posts
    15,103
    Post Likes
    All the same controls can be applied to residential systems if the owner just insists on cooling the place in low ambient conditions....

    I recently added a full load of controls and a windbreak to a system serving an in home theater. With no AC, temps would climb into the 90's in there with all the electronics going, even on cold days.
    RSES Certificate Member
    RSES-SWRA President

    You're not finished learning until you're dead!

  5. #5
    Join Date
    May 2003
    Posts
    22
    Post Likes
    Just curious, I never had to deal with home with a media room. How would you calculate the heat gain of all the electronic equipment.

  6. #6
    Join Date
    Mar 2004
    Location
    Gone
    Posts
    5,340
    Post Likes
    Originally posted by rycon
    Just curious, I never had to deal with home with a media room. How would you calculate the heat gain of all the electronic equipment.
    Add up the total wattage output of the equipment, and then determine your total BTU’s required to handle the wattage.

    Then perform a Manual J on the structure and input the BTU’s required to cool the electronics.

  7. #7
    Join Date
    May 2003
    Posts
    22
    Post Likes

    Frown

    Thanks,MadeinUSA, I really feel stupid for not knowning better.

  8. #8
    Join Date
    Apr 2005
    Location
    Tampa, Florida
    Posts
    1,680
    Post Likes
    I'm not sure if the consumer-grade audiovisual equipment lists it, but most industrial-grade A/V equipment has BTU output in their specs. Industrail amplifiers usually will list BTU output at idle and at 100% (white noise). A normal listener won't go much past 50%. I'll use wattage as a last resort, because it almost always overestimates it. If you have the luxury of time, measure the actual amp (wattage) draw of the equipment as it would be used. The amps printed on the nameplate on the equipment are usually absolute maximums with some safety factor involved. While more common on commercial jobs, don't forget transformers. I have one site with a 10kva transformer in the same room as the equipment. Major idle heat load from the transformer, even higher heat load with the equipment running.

Posting Permissions