Results 1 to 13 of 29
Thread: Fryer Problems
    May 2010
    Fryer Problems
    Client states fryer will stay on but for only 20min. I am thinking hi-limit or thermostat touching the heat exchanger tubing? Any thoughts? Or thermostat is bad causing hi-limit to trip?
    May 2010
    Dirty pilot orifice causing pilot flame not to contact thermopile
    May 2010
    Thanks man!
    May 2010
    No problem, Glad I could help.
    Mar 2011
    Canada
    i like talking to myself aswell
    Mar 2006
    seems you solved it, on the pitco ones i work on the highlimit kills the pilot, so ill ask them if the pilot goes out when they notice the fryer not working, i always replace the hi-limit and t-start at the same time.
    if the orfice was clogged, then how would it light in begin with?
    May 2010
    orifice wasn't "clogged" but partially restricted not allowing enough gas to the pilot resulting in small pilot flame. I always check hi limit by disconnecting the two leads and touching them together if pilot goes out no problem. If it doesn't... Defective hi-limit
    Oct 2010
    It was a millivolt control fryer. If the pilot isn't strong enough to heat up the thermopile to generate the proper millivolt to open the gas valve then it will not work but will still keep the pilot open. Curious why do you always replace the thermostat and hi limit together? Using a temp gauge will tell you which control really needs replacing.
    May 2010
    Ya I stuck my fluke probe in the oil and monitored the temps to see if it was the thermostat
    Jan 2011
    This check has been tried and tested and works great. You jumper out the Hi-limit, then you make sure the fryer is full of oil and heat it up while monitoring the temperature closely so it won't overheat and to check the t-stat is controlling the temp. this will tell you what parts need replacing. no need to go over 400 - 450 degrees, don't need flames, good luck
    Oct 2010
    Why would you jump out the hi limit? I would want to see if it is failing at a lower temp also. As long as it doesn't fail under the highest setting on the tstat then what is the point?
    May 2010
    x2 to what temp said
    Oct 2010
    Again how would that test a hi limit that fails at lets say 300 degrees?