    YT and YK variable orifice

    If I understand the IOM and M document the condenser liquid level setpoint that the variable orifice is controlling to is a set number selected by the start up tech and it will only deviate from that ONE setpoint if changed. So, to clarify, this target setpoint should not change due to ANY other factors while the chiller is running, and furthermore, lets say the setpoint is 50% the chiller will always try to control to 50%, regardless of anything else going on in the system. Right or wrong?

    r404a

  2. #2
    Join Date
    Jun 2008
    Location
    Houston, TX
    Posts
    48
    Post Likes
    Depending on the flash version on start up the target can change but the true set point stays the same. It is a lot to explain do you have the latest 160.54-M1 (810)

  3. #3
    Join Date
    Sep 2007
    Location
    Somewhere in the world.
    Posts
    1,643
    Post Likes
    The setpoint is set up by most likely who started it and can be ajusted at any time or even disable for any reason , and yes there are circumstances that can effect the way it operates the setpoint once set would not change in those events its just trying to maintain its target setpoint.
    A mind is like a parachute. It doesn't work if it is not open.

    The best part of going to work is coming back home at the end of the day.

    Hard work spotlights the character of people: some turn up their sleeves, some turn up their noses, and some don't turn up at all.

  4. #4
    Join Date
    Oct 2003
    Location
    tidewater, va
    Posts
    2,150
    Post Likes
    thanks for the replies

    r404a