    Quote Originally Posted by VTP99 View Post
    True. Why not add strips in steps as needed to assist the pump. Only use what you need.
    You can do whatever you want. Most heat strip packages come with one sequencer or contactor for each 10 kw of heat. A 15 kw package would have two sequencers and you can stage them if you would like. The problem we run into is people complaining the air coming out of the vents isn't warm enough so we just wire Y1 and Y2 together in the air handler. Now I'm referring more to strip heat only systems and not so much heat pumps. Even though it is code most existing heat pump systems around here don't have enough power to the A/H to get enough heat strips to stage. The technology is definitely there but the customer usually doesn't want to pay extra when what they had before worked just fine.
    Quick reply to this message Reply  

  2. #22
    Join Date
    Apr 2005
    Location
    florida
    Posts
    530
    Post Likes
    Quote Originally Posted by ThirdCoastAC View Post
    You can do whatever you want. Most heat strip packages come with one sequencer or contactor for each 10 kw of heat. A 15 kw package would have two sequencers and you can stage them if you would like. The problem we run into is people complaining the air coming out of the vents isn't warm enough so we just wire Y1 and Y2 together in the air handler. Now I'm referring more to strip heat only systems and not so much heat pumps. Even though it is code most existing heat pump systems around here don't have enough power to the A/H to get enough heat strips to stage. The technology is definitely there but the customer usually doesn't want to pay extra when what they had before worked just fine.
    ....you mean W1 &W2?...... ok i can see your point some what on a straight electric heat that you would want instant heat out of register....but we are talking about heat pumps.... no?....
    Jason J Saylor
    Johnson Controls


    "You will encounter many distractions and many temptations to put your goals aside: The security of a job, a wife who wants kids, Whatever. But if you hang in there, always following your vision, I have no doubt you will succeed.”
    Quick reply to this message Reply  

  3. #23
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Quote Originally Posted by ThirdCoastAC View Post
    A 10kw jeat strip usually draws between 19 and 22 amps. A 20 amp breaker for each 10kw of heat plus the 10 for the fan will cover it. If you worked on them you would know this. It is common knowledge.
    A 5KW rated single phase heater draws between 18 and 22 amps depending on supply voltage at that location.

    I work on them.

    240 volt 5KW=20.83 amps
    240 volt 10KW=41.67 amps
    240 volt 15KW=62.5 amps

    Of course, very few places have exactly 240 volts. And the heaters resistance will change slightly with the temp of the heater as it varies with air flow. So the amp draw will change also.
    Quick reply to this message Reply  

  4. #24
    Join Date
    Jan 2011
    Location
    Lynchburg, VA
    Posts
    72
    Post Likes
    Exactly. You can't get around the physics of it. If your 10 kW strip is only pulling 20A, it is only giving you 5kW of heat unless it is being run at 480v.

    The strips are normally 5kW each and more are added to get to whatever total you need.

    Lower voltage will give lower amps and you take a double hit on power. As an extreme, say you connected these elements to 120v. You cut the voltage in half, the current is also cut in half, this means that the power (Power = V X I) is cut to 25% of initial value (10kW of elements would produce 2.5kW of heat).
    Quick reply to this message Reply  

  5. #25
    Join Date
    Jun 2010
    Location
    Western Nebraska
    Posts
    246
    Post Likes
    Quote Originally Posted by ThirdCoastAC View Post
    A 10kw jeat strip usually draws between 19 and 22 amps. A 20 amp breaker for each 10kw of heat plus the 10 for the fan will cover it. If you worked on them you would know this. It is common knowledge.
    Sorry man. You are wrong. Ohm's law is correct.

    Your memory is close for a 5 kw strip which is what most are. There is typically 4 each 5kw strips in a 20kw package. 2 of these strips are typically energized at a time. More than likely what you are measuring is the amp draw per element, which once again is typically 5kw, not the draw for both elements. It'll come to you over time. You just gotta learn to listen to the old guys. We were in your shoes at one time too!
    Quick reply to this message Reply  

  6. #26
    Join Date
    Dec 2002
    Location
    in a house, Appomattox, Va.
    Posts
    5,598
    Post Likes
    lady parts doctor was doing the change due to complaints in the exam rooms. he didn't have any complaints for the heat
    Col 3:23


    questions asked, answers received, ignorance abated
    Quick reply to this message Reply  

  7. #27
    Join Date
    Jul 2010
    Location
    SE Texas
    Posts
    122
    Post Likes
    Quote Originally Posted by beenthere View Post
    A 5KW rated single phase heater draws between 18 and 22 amps depending on supply voltage at that location.

    I work on them.

    240 volt 5KW=20.83 amps
    240 volt 10KW=41.67 amps
    240 volt 15KW=62.5 amps

    Of course, very few places have exactly 240 volts. And the heaters resistance will change slightly with the temp of the heater as it varies with air flow. So the amp draw will change also.
    Yes,you are completely correct. I apologize for my shortness in my prior post. 20A per 5kw, not 10 kw. And I did mean W1 and W2. Long day at work with some very ignorant customers. Not an excuse however for my rudeness.
    Quick reply to this message Reply  

  8. #28
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Quote Originally Posted by ThirdCoastAC View Post
    Yes,you are completely correct. I apologize for my shortness in my prior post. 20A per 5kw, not 10 kw. And I did mean W1 and W2. Long day at work with some very ignorant customers. Not an excuse however for my rudeness.
    We all have bad days from time to tome. Sometimes you gotta step away from the keyboard for a minute or so before posting.

    Some days I take my own advise.
    Quick reply to this message Reply  

  9. #29
    Join Date
    Jan 2010
    Posts
    45,371
    Post Likes
    Wow...........I was beginning to question my knowledge of electric but then i did the math. As stated Ohm's law and between 210-240 volts 41.66-47.61 amp difference.

    I read his first post on that and let it go. And as usual you guys would not let it ride. Constant policing here. But thats a good thing. Keep everyone in check.
    Good job westval !
    Quick reply to this message Reply  

  10. #30
    Join Date
    Jun 2010
    Location
    Western Nebraska
    Posts
    246
    Post Likes
    Quote Originally Posted by VTP99 View Post
    Wow...........I was beginning to question my knowledge of electric but then i did the math. As stated Ohm's law and between 210-240 volts 41.66-47.61 amp difference.

    I read his first post on that and let it go. And as usual you guys would not let it ride. Constant policing here. But thats a good thing. Keep everyone in check.
    Good job westval !
    Not looking to keep anyone in check, just thinking outloud through the keyboard!......during heating season that's the only time I get to stop and think.....
    Quick reply to this message Reply  

  11. #31
    Join Date
    Jun 2001
    Location
    Moore, Oklahoma, United States
    Posts
    4,648
    Post Likes
    If there is enough amperage to the air handler you could let the thermostat use 10KW for AUX heat and use the other 5KW for defrost. Most air handlers just need a simple wiring change to set them up that way, connect W1 to the thermostat, W2 to the white/defrost from the condenser. If the heat pump can't keep up then only 10KW of heat would be added instead of the full 15KW. If the temp dips too much with only 5KW in defrost the thermostat will bring on the 10KW aux heat for a total of 15KW. Wiring this way has some potential to save some $$$ in defrost at the expense of cooler air from the registers.
    Quick reply to this message Reply  

  12. #32
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Old thread, closed as too many previous posters are not Pro * members.
    Quick reply to this message Reply  

Page 2 of 2 FirstFirst 12

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •