    How do you determine the pressure drop across a coil?

  2. #2
    Join Date
    May 2005
    Location
    Mississippi
    Posts
    102
    Post Likes
    Manufacturer should have a specification sheet/chart available.

  3. #3
    Join Date
    Dec 2004
    Location
    CA. in transition to NJ.
    Posts
    28
    Post Likes
    To determine drop accross an "A" coil you simply drill a hole big enough for a temp probe between the two coils WATCH FOR TUBING, and then drill another above but close to the coil nearest the supply duct. Let the unit run in whatever mode you choose but put the t-stat on a good high setting in order to keep it from becoming satisfied to quickly. After about 10 minutes of run time measure the two temperatures and subtract to get the difference or "THE DROP" accross the coil. Keep well in mind however that you must check all air filters, all air registers, and the blower for cleanliness and no blockege anywhere. If the unit is equiped with a humidifer dont let it rn during the check. I hope this info helps you, For more info you can order a book called HVAC service procedures from either Honeywell or Carrier.

  4. #4
    Join Date
    May 2000
    Location
    Indianapolis, IN, USA
    Posts
    42,886
    Post Likes
    Need a manometer or magnahelic. Take positive pressure reading above & below the coil. The diff is the drop over the coil. Coil should be wet!

  5. #5
    Join Date
    Aug 2002
    Location
    Office and warehouse in both Crystal River & New Port Richey ,FL
    Posts
    18,835
    Post Likes
    If it's an air handler the readings will be negative instaed of positive.

  6. #6
    Join Date
    Dec 2004
    Location
    CA. in transition to NJ.
    Posts
    28
    Post Likes
    AirFlow Measurment- Pressure Drop Method
    1. Drill a quarter inch hole on either side of the evap coil. If it is a slab coil then one hole goes above the coil and the other goes below the coil but, keep both in the center as much as possible, ang be careful not to drill into nearby piping or the coil. If it is an "A" coil put one hole in the middle of the A and the other above the A on the side nearest the supply duct.

    2. Turn the unit on and set the t-stat so that the compressor and systm blower run continuosly during the measurement.

    3. Level the inclined manometer. Insert a quarter inch tube about 2 inches in each hole. Seal the tubes at the insertion points. Connect the open ends of the tubes to the manometer. The tube from the hole at the output side of the coil should be connected to the lower end of the monometer.

    4. Read and record the static pressure drop across the coil.

    5. Compare the reading to the performance data supplied by the manufacturer.

    Always remember to make sure that the system air filter is clean, the blower wheel is clean , the evap coil is clean, there are no loose or worn belts on belt drives and that belt tension is right, and that the blower rotates in the proper direction.

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •