Results 1 to 9 of 9
Thread: CFM Formula
    May 2005
    I'm trying to remember the formula for calculating the CFM of a indoor split system air handler. I know that you're supposed to take the amp draw of the unit, and the delta T between the supply and return, but what is the formula that you plug you info into to figure out how much CFM you are getting across the coil/heat strips? HELP ME PLEASE!
    CFM = Load / 1.1 x TD
    This is a sensible heat equation for airflow requirements.
    Is it the one you are asking about?
    South/West of Quebec in the other part of Canada
    CFM = volts x amps x 3.414 / 1.08 x temperature rise
    Apr 2005
    Chillbilly;
    I your TD the same as delta Temp across the evap?
    What about the CFM for a gas furnace?
    thanks
    gn
    CFM = btu output/ 1.08 x temperature rise
    P.S. your temp rise is not across the evap, it is across the heating elements or heat exchanger.
    P.P.S. volts x amps x 3.414 = btu output on electric furnace
    [Edited by key on 05-18-2005 at 06:46 AM]
    May 2005
    Smile
    That's the one. Thanks a million.
    The accuracy of the measurements can make a large difference,using this method.
    A manometer and fan data chart,is a lot easier and more accurate,IMHO.
    I fooled with those calculations to determine CFM several years ago, I finally gave up and went and bought a good quality Pitot tube airflow tester, a good traverse on the main supply trunk will eliminate all the guess work.
    When you give a lesson in meanness to a critter or a person, don't be surprised if they learn their lesson.
    Jul 2010
    CFM testing problem
    In my refigeration book the cfm calc formula is CFM=BTUH/1.1XTD on my test they used BTUH input (Not Output) and at sea level. What is up with this.
    I have also seen 1.0505 and 1.08 as numbers in the formula. At any rate my answers were not the same as those given to chose from.