Results 1 to 4 of 4
  1. #1
    Join Date
    Aug 2002
    Posts
    8
    Post Likes
    I'm a home inspector and came across something I have never noticed before. The air conditioning compressor was placarded "max fuse amp 40A". The breakout box had a fuse block rated at 60A. The disconnect at the main service panel to the house for the compressor was 40A. Is this normal?
    Thanks in advance,
    Jeff

  2. #2
    Join Date
    Dec 2002
    Location
    SouthEast NC ICW & Piedmont Foothills
    Posts
    7,711
    Post Likes
    Nothing wrong with that.
    perfectly legal, as long as wire is sized correctly.
    only two sizes of fuse blocks 30 & 60, the fuses change physical size from 30 to 35.


    you can`t slap a piece of copper pipe in the place of a fuse, thats against disconnect manufacturers design.
    It`s better to be silent and thought the fool; than speak and remove all doubt.

  3. #3
    Join Date
    Jul 2001
    Posts
    3,112
    Post Likes
    So how did you identify what you found on your inspection report? Try finding an electrician locally you can ask this type of question. Make sure you are providing a professional, accurate home inspection.

  4. #4
    Join Date
    Feb 2003
    Location
    S.W. PA
    Posts
    3,298
    Post Likes
    the 40 amp breaker is to protect wire
    breakers are in place to keep wire from overheating and starting a fire
    disconnect is in place to allow for quick disconnect for power to unit when being serviced

    make sure that breakers are always sized to wire
    breakers and fuses are not in place to protect appliance at least not to the point that alot of people think they are.