Distech ECB-203
I know on some of the Distech LON controllers some of the Network Variables were many to one and I would use those to tie all my terminal loads in and it would give me min/max/avg, my question is are there any points like this on the bacnet controllers?
-
02-22-2011, 11:36 PM #2
Member
- Join Date
- Oct 2010
- Location
- Montana
- Posts
- 71
-
05-05-2011, 06:04 PM #3
Regular Guest
- Join Date
- Apr 2011
- Location
- Ottawa, ON
- Posts
- 24
You may have already figured this out, but there is a block for this. It's called "NetInMinMaxAvgSum_1.1"
You can find it in the Code Library under:
gfxApplications -> 1.1 -> BACnet -> NetworkValue(ForLoop)
instead of using a "Network Variable Input" you use "Network Value". This block will return Min,Max,Avg,Sum as well as the total valid points, which is good because this block will omit an invalid point so that your average is still OK.
Cheers