    Auxiliary Heat stays on went outside temperature above freezing

    I have a new (October 2009) carrier heat pump & Edge programmable thermostat with the setting for the check valve (08) at 40, and the smart recovery setting on (12). Even when the temperature is in the high thirties, and forties up to 45 the auxiliary heat keep coming on especially early in the morning and throughout the day. The preset setting70°from 7 a.m. -- 11 a.m., 65°11 a.m. -- 5 p.m., & 65°11 p.m. -- 7 a.m.

    Why does the auxiliary heat keep coming on?

  2. #2
    Join Date
    Mar 2007
    Location
    Myrtle Beach, SC
    Posts
    2,851
    Set the thermostat on hold so it does not set back. Email me and I will send you instructions by return email. my email address is in my profile.
    Remember, Air Conditioning begins with AIR.

  3. #3
    Join Date
    Jun 2008
    Location
    CT
    Posts
    45
    Adjust your second stage on the thermostat that should fix that or add in the carrier auxillary heat lock out sets up as sens1

  4. #4
    Join Date
    Sep 2002
    Location
    I don't know
    Posts
    2,888
    Hit hold and set it to 70F.

    If the aux heat still comes on in mild weather, get the charge checked.