    Small walk in freezer

    Called to look at an old inop walk in freezer. No info on history. Semi hermetic k body m#kaa2-0075-cav. Says 12/22/502
    Singer evap m#dh2-21-2
    Box 4x5x5.

    Question is not knowing what refer is in here etc.. Can it run fine on either 12/22/502 depending on what txv is installed? It's a flare txv, easy to access and change. What would you do.? The info on compressor from the opi page says its a cfc12 low temp. Doesn't mention the other refers. Reciever and coil also say 12/22/502. Don't have experiance with these multi rated compressors. Thanks

  2. #2
    Join Date
    Aug 2002
    Location
    Southold.calm
    Posts
    6,364
    The compressor or evap says 22/22/502?
    See what valve is in there.

  3. #3
    Join Date
    Mar 2013
    Location
    swan valley idaho
    Posts
    732
    I was not able to see anything on powerhead. Do I have the option to use 22 if i put a 22 txv in as well? Is that the idea on these dual rated k body's?

  4. #4
    Join Date
    Aug 2002
    Location
    Southold.calm
    Posts
    6,364
    From copelands web site
    R-12 low temp
    https://opi.emersonclimate.com/was.e...web/OPIServlet
    Sign up on the Emerson web site and you can get the print out.

  5. #5
    Join Date
    Mar 2013
    Location
    swan valley idaho
    Posts
    732
    I noticed the printout shows r12 low temp also. That's why I'm confused. The actual metal nameplate on compressor says r12/22/502? If its 12 only, i can't do much. I'm not buying new refrigerant for one job. I carry 134,404,416a,22 now. I thought if it was dual rated for 502 as well, i would get a 404 txv and try that? 134a being the other choice, i don't think is the best for a freezer.

  6. #6
    Join Date
    Aug 2002
    Location
    Southold.calm
    Posts
    6,364
    R-134A is not an option.
    I believe MP-66 is the best replacement for R-12 in low temp applications

  7. #7
    Join Date
    Aug 2006
    Location
    st.petersburg,fl
    Posts
    806
    Quote Originally Posted by pecmsg View Post
    R-134A is not an option.
    I believe MP-66 is the best replacement for R-12 in low temp applications
    You are 100% correct MP-66 is the best for low temp 12...
    Isn't sanity just a one-trick pony anyway? I mean, all you get is that one trick, rational thinking, but when you're good and crazy, well, the sky's the limit!

  8. #8
    Join Date
    Aug 2006
    Location
    st.petersburg,fl
    Posts
    806
    See what valve is in the unit, possibly stamped on valve body depending on age and valve. You can alway swap out valve and put 408 in it and be done with it.

    Hope this helps.
    Isn't sanity just a one-trick pony anyway? I mean, all you get is that one trick, rational thinking, but when you're good and crazy, well, the sky's the limit!

  9. #9
    Join Date
    May 2014
    Location
    Bay Area California
    Posts
    1,944
    Quote Originally Posted by kklobas View Post
    I noticed the printout shows r12 low temp also. That's why I'm confused. The actual metal nameplate on compressor says r12/22/502? If its 12 only, i can't do much. I'm not buying new refrigerant for one job. I carry 134,404,416a,22 now. I thought if it was dual rated for 502 as well, i would get a 404 txv and try that? 134a being the other choice, i don't think is the best for a freezer.
    So you want something for 'freezer' applications? It used to be very common for Copeland compressors to be rated for R-12 high temp and R-502 low temp. R-502 pressures are pretty much the same as R-22, so that nomenclature plate doesn't throw up any alarms for me; and if I'm not mistaken, R-502 is R-22 with another refrigerant added for better oil return at low temps.

    Basically, on the surface, that compressor can handle R-404a for a freezer application.

    If it is still a self contained unit, and we're talking an old school unit, check the temp pressure relationship in maybe early morning. R-12 will be obvious. There is a bit of difference between R-22 and R-502, but enough to make it easy.

    Or you could just see if it is outfitted with defrost heaters and a time clock . . . That might be your first clue . . .

  10. #10
    Join Date
    Aug 2006
    Location
    st.petersburg,fl
    Posts
    806
    Quote Originally Posted by BBeerme View Post
    So you want something for 'freezer' applications? It used to be very common for Copeland compressors to be rated for R-12 high temp and R-502 low temp. R-502 pressures are pretty much the same as R-22, so that nomenclature plate doesn't throw up any alarms for me; and if I'm not mistaken, R-502 is R-22 with another refrigerant added for better oil return at low temps.

    Basically, on the surface, that compressor can handle R-404a for a freezer application.

    If it is still a self contained unit, and we're talking an old school unit, check the temp pressure relationship in maybe early morning. R-12 will be obvious. There is a bit of difference between R-22 and R-502, but enough to make it easy.

    Or you could just see if it is outfitted with defrost heaters and a time clock . . . That might be your first clue . . .
    If you try to use R-22 In that compressor for a low temp application you will destroy it.

  11. #11
    Join Date
    May 2014
    Location
    Bay Area California
    Posts
    1,944
    Quote Originally Posted by skpkey9 View Post
    If you try to use R-22 In that compressor for a low temp application you will destroy it.
    When did I say R-22 was appropriate for a low temp app. ?

  12. #12
    Join Date
    Aug 2006
    Location
    st.petersburg,fl
    Posts
    806
    Quote Originally Posted by BBeerme View Post
    When did I say R-22 was appropriate for a low temp app. ?
    Re- read your last post ...
    Isn't sanity just a one-trick pony anyway? I mean, all you get is that one trick, rational thinking, but when you're good and crazy, well, the sky's the limit!

  13. #13
    Join Date
    Aug 2002
    Location
    Southold.calm
    Posts
    6,364
    Here is the report i was looking for
    Attached Images Attached Images

Page 1 of 3 123 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event