    What abnormal operating data (high head pressure, low superheat, etc) would lead you to conclude there is air in a split system?

  2. #2
    Join Date
    Aug 2003
    Fort Worth, TX
    Post Likes
    I would gather more data than just high head/low superheat before concluding non-condensables are in the system.

    High head/low superheat can be present in a system that is clean internally (no moisture or non-condensables) but has dirty outdoor coils and restricted airflow inside. If anything, non condensables when they reach the metering device would enter the evap and rob space from the refrigerant to do its work.
    Evap pressure would likely run higher than normal due to non condensables (law of partial pressures), aggravated by high head pressure and a high pressure stacked against the metering device. Higher evap pressures is a condition not often associated with low superheat (due to airflow problems), unless the system is ridiculously overcharged and the mass flow rate is mostly responsible for the low superheat.
    Building Physics Rule #1: Hot flows to cold.

    Building Physics Rule #2:
    Higher air pressure moves toward lower air pressure

    Building Physics Rule #3:
    Higher moisture concentration moves toward lower moisture concentration.

  3. #3
    Join Date
    Sep 2004
    Post Likes
    I am not sure if there is definitive answer since systems are different. It could be either thermal/pressure or thermistor controlled expansion devices or fixed orfice. Each one would be affected differently. I had a 10 year old miller/nordyne 2 1/2 ton split system (fixed orfice) the other day, I could not get any good readings superheat and subcool readings were way off not even close, the superheat reading was within 2 degrees of saturation with no change after recovering most of the charge. I finally just recovered ALL the refrigerant/evacuated and recharged with virgin R22. The only conclusion that I could come to was that someone had topped the system off with some weird refrigerant (possible R134A as it seemed to have a higher temp to pressure ratio) obviously it was not R22/or it had air in the system big time maybe?. Everything was good after recharge perfectly normal readings. Could have been air? I do not have a refrigerant identifier I wish I did it is on my wish list. If you are having weird readings I would suggest recharge with known good refrigerant kinda like these silly computers if they get corrupted sometimes you have to drain the juice and restart them LOL
    When you give a lesson in meanness to a critter or a person, don't be surprised if they learn their lesson.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts

Related Forums

Plumbing Talks | Contractor MagazineThe place where Electrical professionals meet.