Results 1 to 8 of 8
Thread: Smokey House
-
02-01-2011, 08:10 PM #1
Smokey House
When the wind is blowing really hard and constantly, the smoke from my fireplace reverses and enters my home, setting off the smoke alarms and filling my house with smoke. My question, does the height of the chimney need to be higher than the roof ridge? I know if a flue pipe is not higher than the roof ridge a high wind will trip the pressure switch on a gas furnace. So before I spend the money to extend the chimney, I thought I would ask if it will stop the wind from blowing down the chimney.
-
02-02-2011, 07:43 AM #2
Professional Member
- Join Date
- Mar 2001
- Posts
- 1,213
Rule of thumb...chimney 2' higher than any point within 10'.
-
02-02-2011, 09:28 AM #3
-
02-05-2011, 08:52 PM #4
Professional Member*
- Join Date
- Oct 2009
- Location
- Kingsport, Tennessee
- Posts
- 129
FYI. Moose is right.
Here is the building code from the IRC 2003 for exact wording.
R1001.6 Termination. Chimneys shall extend at least 2 feet higher than any protion of a building within 10 feet, but shall not be less than 3 feet above the hightest point where the chimney passses through the roof.

jt
-
02-06-2011, 07:08 AM #5
thanks
-
02-21-2011, 04:08 PM #6
Regular Guest
- Join Date
- Jan 2011
- Location
- WI
- Posts
- 11
Glad I found this thread!
We just moved into a place with a natural fp which worked fine last month. Tried a fire yesterday with 30-mph winds and now the whole house reeks of woodsmoke. I'll have to look at the chimney when I get home.
-
02-21-2011, 05:03 PM #7
I found extensions in 3 ft lenghts at Lowes. price 69-84$$
-
02-21-2011, 05:19 PM #8
Professional Member*
- Join Date
- Sep 2005
- Location
- North GA
- Posts
- 17,287
Hearthman should be along soon... He will have the details (from both code and experience).
GA-HVAC-Tech
Galatians 2:20-21; Colossians 1: 21-22 & 26-27; 3:1-4; Romans Ch's 5-6-7-8
2 Chronicles 7:14
Quality work at a fair price with excellent customer service.


Reply With Quote