Results 1 to 7 of 7
    I had a discussion recently w/ a tech. guy from a local supplier about charging new installs. We always weigh-in are charges (units comes w/ enough refrigerant for 15' of liquid line, over that ,add .6 oz. for every 1' of liquid line ) he liked the superheat/subcool methods. To me, weigh-ins are fool proof ( if ya got a accurate scale ), and faster. Why do s.h. or subcool when your startin fresh.any thoughts??
    I don't trust the factory to have the base charge right
    South Dakota
    Weighing in the charge is best for self-contained systems where you actually know the correct charge. Superheat and subcooling for all others.
    Tyler, TX
    Also, if there is a flow issue, like wrong orifice, fan speeds, etc, you can catch it.
    RSES Certificate Member Specialist
    Southwest Regional Association of RSES Secretary, 2017
    Loonie,I can understand the factory charge being off. I think.
    bwal2,how does fan speed determine charge?? alot of are new units are variable speed, and TXV.
    Tyler, TX
    And a lot of them are not.
    Would heat load have any bearing on charge?
    If you have inadequate airflow, superheat will be low, even with a perfect factory charge.
    That includes packaged units hooked up to a tiny filter grill.
    Without airflow, you don't have heat to evaporate your refrigerant.
    Austin, TX
    You normally weigh in charges on small appliances,
    and car/truck air conditioners. You have to weigh
    in charges when it is cold, no other way to reliably
    charge properly when cold. Split a/c systems are
    difficult to weigh in because you do not know how
    long the lineset is, and the data plate is seldom
    correct.