    Six circuit DX M-Coil on a 3T Rheem 10 SEER Heat Pump. Numbering the circuits starting closest to the camera, #3 is sweating to the header maybe #6 too. All the others less or all dry.

    RA DB 75F
    RA WB 64F

    EST 49F

    Header Exit SH 23F (Line 72F) **no hunting / hysteresis**
    Circuit #1 SH 20F (Line 69F)
    Circuit #3 SH 8F (Line 57F)

    Uneven distributor feed?
    Uneven airflow / circuit loading?
    oil logging?


  2. #2
    Join Date
    Jun 2003
    Location
    GA
    Posts
    395
    Post Likes
    Thread Starter

    Hmm circuit problems?

    Psych chart indicates DP 58F.
    That explains latent on #3 only.

    Do any of you's guys (or the two yutes) specifically look for sweat patterns or tape a bead type TC to the circuit ends to isolate for circuit problems?




  3. #3
    Join Date
    Aug 2002
    Posts
    6,047
    Post Likes
    Your gonna have to open er up and see what is wrong.


  4. #4
    Join Date
    Jun 2003
    Location
    GA
    Posts
    395
    Post Likes
    Thread Starter

    Talking

    yeah. I figured I'd play with it first and learn something since it's mine.

  5. #5
    Join Date
    Aug 2004
    Location
    North Richland Hills, Texas
    Posts
    15,630
    Post Likes

    Re: circuit problems?

    Originally posted by mdman
    Psych chart indicates DP 58F.
    That explains latent on #3 only.

    Do any of you's guys (or the two yutes) specifically look for sweat patterns or tape a bead type TC to the circuit ends to isolate for circuit problems?
    I use a Fluke surface probe for checking out the circuits on a coil that I suspect a problem on. Some tubes not sweating while the rest of them are is a good clue that something is not right.

    I have seen a few coils that seemed to be feeding unevenly that had refrigerant pressures, SH and SC right on the money per the manufacturers specs for the operating conditions though.

  6. #6
    Join Date
    Jun 2003
    Location
    GA
    Posts
    395
    Post Likes
    Thread Starter

    Question 80PK-7

    Originally posted by mark beiser
    Originally posted by mdman
    Psych chart indicates DP 58F.
    That explains latent on #3 only.

    Do any of you's guys (or the two yutes) specifically look for sweat patterns or tape a bead type TC to the circuit ends to isolate for circuit problems?
    I use a Fluke surface probe for checking out the circuits on a coil that I suspect a problem on. Some tubes not sweating while the rest of them are is a good clue that something is not right.

    I have seen a few coils that seemed to be feeding unevenly that had refrigerant pressures, SH and SC right on the money per the manufacturers specs for the operating conditions though.
    Do you use the 80PK-7 ?

  7. #7
    Join Date
    Aug 2004
    Location
    North Richland Hills, Texas
    Posts
    15,630
    Post Likes
    No, I have the 80PK-3, really fast response from it. Had it for years, it is the 80PK-3A now, not sure what they changed about it though

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Related Forums

Plumbing Talks | Contractor MagazineThe place where Electrical professionals meet.