  1. #1
    Join Date
    May 2005
    Posts
    14
    working on a resturant doing some relocation work and the owner asked a question that control wise i wasnt to sure about, he asked if he could put an additional heat/cool unit on the dinning side to help with an occasional problem of the resturant on the hottest days being a little under powered, that was easy enought to firgure,except he only wants the new unit to run when the other one cant keep up.that where im stumped,is there a t-state that does that or are we talking a bunch of controls?

  2. #2
    Join Date
    Jul 2001
    Location
    Canada
    Posts
    1,818
    Just set the supplimental units TSTAT higher than the primary unit.

  3. #3
    Join Date
    Nov 2000
    Location
    Eastern PA
    Posts
    68,962
    A two stage cooling stat with the Y2 and common to an isolation relay controlling the Y and R of the supplemental unit will also work.
    Government is a disease...
    ...masquerading as its own cure…
    Ecclesiastes 10:2 NIV


  4. #4
    Join Date
    May 2005
    Posts
    14
    i guess i was thinking about a dual stage t-state a control guy was messing with on another job,maybe they had more units or a different problem? thanks for the reply