flue pipes for hot water heater and furnace
does it matter which pipe is over the other pipe,my hot water heater flue pipe is under the furnace flue pipe venting thru the chimney,does that have to be switched so the higher pressure flue pipe of the water heater is above the furnace flue pipe,or does it really make any difference,thanks
-
02-16-2011, 07:58 AM #2
If you have any concerns I recommend seeing if there is a record of a permit on either appliance. Probably not. I then recommend buying a permit. The building inspector will verify the safety of your installation. Safety is more important than "free".
"I have never let my schooling interfere with my education."
Mark Twain
More at: http://www.quotationspage.com/subjects/education/
-
02-16-2011, 07:59 AM #3
Professional Member*
- Join Date
- Jul 2006
- Posts
- 967
Here's the book
http://www.duravent.com/pdf/shbook.pdf
-
02-16-2011, 08:02 AM #4
Regular Guest
- Join Date
- Jan 2010
- Location
- Athens GA
- Posts
- 1,234
Wye are you so confused,doesn't the smaller pipe go into the larger pipe?
The larger btu goes stright into the chimney and the smaller btu meets it at the corner,,,thats wye.
-
02-16-2011, 10:12 AM #5
Professional Member*
- Join Date
- Dec 2010
- Location
- The Quad-Cities area (midwest).
- Posts
- 1,746
-
02-16-2011, 12:19 PM #6
Regular Guest
- Join Date
- Jul 2007
- Posts
- 79
why exactly does the water heater flue pipe have to be over the furnace flue pipe
-
02-16-2011, 02:20 PM #7
Professional Member*
- Join Date
- Dec 2010
- Location
- The Quad-Cities area (midwest).
- Posts
- 1,746
-
02-16-2011, 04:04 PM #8
Regular Guest
- Join Date
- Jul 2007
- Posts
- 79
ok it vents better,is there any issue with gasses from the water heater finding their way to the furnace thru the furnace flue,thanks
-
02-16-2011, 04:41 PM #9
Regular Guest
- Join Date
- Jan 2011
- Location
- Huntley, IL
- Posts
- 25
It would take a really strong downdraft in the chimney to push the water heater gases down, into the furnace vent connector and then into the furnace. It will only rarely happen- assuming the house isn't negatively pressurized by some other piece(s) of equipment...
-
02-16-2011, 05:07 PM #10
Professional Member*
- Join Date
- Dec 2010
- Location
- The Quad-Cities area (midwest).
- Posts
- 1,746
-
02-16-2011, 06:43 PM #11
the OP is a DIYer...check his other threads. now he needs help. Ban him.
FILL OUT YOUR PROFILE!!
-
02-16-2011, 06:58 PM #12
Borderline.
But there are a lot of issues you can have. CO at the top. Have it checked by someone who knows how.
-
02-16-2011, 07:18 PM #13
It is dangerous to advise on flue piping. How do you know that the flue is located per code on the ceiling or is double wall where it needs to be or any other of a dozen subtle errors?
Let him call a pro. He probably has no desire to have his installation inspected as I suggested. Cest la vie.