Results 14 to 18 of 18
Thread: Carrier 30gxr
-
02-18-2011, 04:02 PM #14
Professional Member*
- Join Date
- Aug 2002
- Location
- Greenville SC
- Posts
- 398
15% is what it is set at from the factory. On these chillers you will get a lot of nuisance trips at that setting. I always set them at 20-22% and have never had any problems. I have been told by the Carrier 30 series guru that he has no problem at setting them up to 30%. You can only set them up to 30% with latter software.
-
02-18-2011, 06:11 PM #15
Professional Member
- Join Date
- Feb 2007
- Location
- So. Cal.
- Posts
- 42
Another ? What size is the Allen key I need to change the internal oil fliter on the screw compressor? It looks close to 1/2 inch
-
02-18-2011, 06:18 PM #16
Professional Member*
- Join Date
- Jan 2008
- Location
- Dallas ,Texas
- Posts
- 3,512
-
02-18-2011, 07:12 PM #17
Professional Member
- Join Date
- Feb 2007
- Location
- So. Cal.
- Posts
- 42
3/4" ok also what seals the end is it a o-ring or just a machine seal?
-
02-21-2011, 07:19 AM #18
Professional Member*
- Join Date
- Aug 2002
- Location
- Greenville SC
- Posts
- 398
Takes an O-ring. Make real sure the internal checkvalve is holding before you unscrew the plug. Sometimes the plug can be very hard to unscrew the first time.


Reply With Quote