Results 14 to 18 of 18
Thread: Carrier 30gxr
    Greenville SC
    15% is what it is set at from the factory. On these chillers you will get a lot of nuisance trips at that setting. I always set them at 20-22% and have never had any problems. I have been told by the Carrier 30 series guru that he has no problem at setting them up to 30%. You can only set them up to 30% with latter software.
    Feb 2007
    So. Cal.
    Another ? What size is the Allen key I need to change the internal oil fliter on the screw compressor? It looks close to 1/2 inch
    East of big city prices.
    Quote Originally Posted by fordtrucksrule View Post
    3/4" and lots of rags if you don't do it right.
    Feb 2007
    So. Cal.
    3/4" ok also what seals the end is it a o-ring or just a machine seal?
    Greenville SC
    Takes an O-ring. Make real sure the internal checkvalve is holding before you unscrew the plug. Sometimes the plug can be very hard to unscrew the first time.