Thread: Carrier 30gxr

  1. #1
    Join Date
    Feb 2007
    Location
    So. Cal.
    Posts
    58

    Carrier 30gxr

    Hey i have a carrier 30gxr225f611cl ecologic r-134a screw chiller today i walked up to it today to 4 alarms those were a152 (down due to failure) t055 (compressor b1 failure no current) and t052 and t051 (compresor a1 and a2 off due to current unbalance. I first checked the wireing to the klixon module 3 in total and check them to the mail control board and all connections were good. then i reset the chiller and got compressors a1 and b1 to come on and i check for voltage imbalance and amprage imbalance at the klixon modules and ch power at disconnect all were below 5% devation Any other ideas?

  2. #2
    Join Date
    Jan 2008
    Location
    Dallas ,Texas
    Posts
    3,720
    Loose connections or you really had some sort of weird power issue with all 3 compressors going flaky.
    UA 100

    It takes three people to do anything around here. Two do the work, one explains to the crowd of people who showed up when they seen smoke and flames.

  3. #3
    Join Date
    Feb 2007
    Location
    So. Cal.
    Posts
    58
    I had this same issue at about 3 weeks ago and i found one of the 0/1 wires going to compressor a1 at the crimp connection was bad and corroding. i had the same issue 3 weks ago same codes. ive check the contactior and check voltage drop across and they were under .03v across the contactors, so i know the contactors are good any other ideas

  4. #4
    Join Date
    Jan 2008
    Location
    Dallas ,Texas
    Posts
    3,720
    Quote Originally Posted by fordtrucksrule View Post
    I had this same issue at about 3 weeks ago and i found one of the 0/1 wires going to compressor a1 at the crimp connection was bad and corroding. i had the same issue 3 weks ago same codes. ive check the contactior and check voltage drop across and they were under .03v across the contactors, so i know the contactors are good any other ideas
    Not unless someone changed the imbalance setpoint and you haven`t changed out a starter lately, it is wye delta right?
    UA 100

    It takes three people to do anything around here. Two do the work, one explains to the crowd of people who showed up when they seen smoke and flames.

  5. #5
    Join Date
    Feb 2007
    Location
    So. Cal.
    Posts
    58
    yes it is a wye delta starter. as far as i know no one has messed with the parameters.

  6. #6
    Join Date
    Dec 2010
    Location
    Central US
    Posts
    427
    A1 & A2 compressor "unbalance setpoint should be 15% default" it alarms after a continuous 15% or more for 25 minutes.

    B1 "no current" if there is a call for B1 comp and there is no amp draw on all 3 legs for more than 3 seconds it will alarm.

    Are than any other alarms in history log? power fails, phase loss etc.. Thats pretty strange, might be the beggining of a board problem.

    Might check primary connections and voltages to transformers serving Klixon modules (CCP's) and secondary connections and voltages. could also be a transformer problem. It would be more logical if there are not any other alarms in history log. especially because it is with 3 compresors and it is on the amperage side (alarms) with no voltage alarms
    Last edited by emcontrols; 02-15-2011 at 11:46 PM.

  7. #7
    Join Date
    Feb 2010
    Location
    MEXICO
    Posts
    472
    which is the voltage deviation? could give more details? readings of voltage and amperage

  8. #8
    Join Date
    Feb 2007
    Location
    So. Cal.
    Posts
    58
    The voltages are as flopped 477 479 482 ave is 479 so max devation is 3 volts on l3 and 2 volts on line 1

  9. #9
    Join Date
    Feb 2010
    Location
    MEXICO
    Posts
    472
    amp?

  10. #10
    Join Date
    Feb 2010
    Location
    MEXICO
    Posts
    472
    the percentage of voltage imbalance is 0.6%
    where maximum deviation 3volts x 100 = 300/479 = 0.626%

  11. #11
    Join Date
    Aug 2002
    Location
    Greenville SC
    Posts
    432
    The voltage imbalance setting can cause you to have alot of nuisance trips on the 30HX and 30GX chillers . It will not hurt anything to set it up to 22%. If you still have trips set it higher.

  12. #12
    Join Date
    Feb 2007
    Location
    So. Cal.
    Posts
    58
    ok the amp draws are as follows 76.4 78.8 and 81.4

  13. #13
    Join Date
    Feb 2010
    Location
    MEXICO
    Posts
    472
    the% current imbalance is 3.29 is thenormal, maximum by the plant is 15%, check electrical connections to the module cpm.etc

Page 1 of 2 12 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event