Thread: Carrier 23xl
-
02-13-2011, 07:28 PM #1
New Guest
- Join Date
- Feb 2011
- Posts
- 3
Carrier 23xl
Hi Folks,
I'm new here and it's my first post. I'm from Brazil and need Help in a Carrier 23XL that i'm working on.
Actually machine is running but i have a alert message "High condenser pressure". I read some parameters that may help all:
Evaporator Refrig temp: 11,3c
Evaporator Pressure: 606,8 Kpa
Condenser Refrig Temp: 41,6c
Condenser Pressure: 1490,7Kpa
Discharge Temp: 56,8c
Oil Sump Temp: 56,8c
At Pic II i also have:
CHW in: 18,3c
CHW out: 15c
CDW in: 27c
CDW out: 34c
MTR AMP 80%
So if any one have ideas to help my chiller i would apprechiate a message.
Thanks in advanced!
-
02-13-2011, 07:36 PM #2
are your tubes clean and condenser water flow correct?
-
02-13-2011, 08:47 PM #3
Your Condenser approach
I would be looking at dirty or blocked tubes as your condenser approach is almost 14*F (8*C) . How many pass is your condenser, you may be by-passing water through a division plate. Just a few ideas -GEO