    Problems with Trane XC95

    Just installed a Trane TUHM060. Venting with 3", LP converted. When unit fires up at 65% the valve is throttling rapidly, after about 3 min the outlet pressure has reduced to 0"wc and unit shuts down. The in coming pressure also throttles between 11" and 15" but seem to be caused by the furnace gas valve. if I disconnect the pressure hose on the positive pressure port a gas valve, the unit will run( still throttling) but pressure doesnt drop. After about 8 mins and unit reaches 70% capacity the pressure smooths out and unit runs great. I can only achieve this with that pressure hose disconnected from the gas valve though.

  2. #2
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Its not the gas valve.

  3. #3
    Join Date
    Jun 2006
    Location
    New Jersey
    Posts
    4,456
    Post Likes
    Quote Originally Posted by beenthere View Post
    Its not the gas valve.
    And I've been warned about given hints in the public forums.

  4. #4
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Quote Originally Posted by ascj View Post
    And I've been warned about given hints in the public forums.
    But I didn't tell him to check the flux capacitor, so I think I'm safe.

  5. #5
    Join Date
    Oct 2009
    Location
    Virginia
    Posts
    48
    Post Likes
    Thread Starter
    Just trying to get a couple ideas before I call Trane on Monday. Nothing I cam do until then anyway. I appreciate it

  6. #6
    Join Date
    Oct 2009
    Location
    Virginia
    Posts
    48
    Post Likes
    Thread Starter
    What happened to this site? Techs could talk to other techs, i guess I'm not cool enough to talk to the big boys anymore. You guys rock!

  7. #7
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    They still can. Just for the last 4 or 5 years, its done in the pro forums.

  8. #8
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Your not registered under 2 names are you.

  9. #9
    Join Date
    Oct 2009
    Location
    Virginia
    Posts
    48
    Post Likes
    Thread Starter
    I signed up originally around 2000 and forgot my password and username, I had to open a new account, I think I got booted do to inactivity

  10. #10
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    I see there is another account from the same company. Signed up in June 2009 I believe.

  11. #11
    Join Date
    Oct 2009
    Location
    Virginia
    Posts
    48
    Post Likes
    Thread Starter
    I am not sure, I see the link to apply for professional membership. So I will do that.

  12. #12
    Join Date
    Oct 2009
    Location
    Virginia
    Posts
    48
    Post Likes
    Thread Starter
    FYI. Trane is developing a new LP gas valve to fix this problem. Fix for now is to set thermostat to single stage operation.

  13. #13
    Join Date
    Aug 2010
    Location
    N.E. Indiana
    Posts
    45
    Post Likes
    FYI, I believe the new gas valve for propane is available now. May cure your problem. Ask dealer about new valve.

  14. #14
    Join Date
    Oct 2009
    Location
    Virginia
    Posts
    48
    Post Likes
    Thread Starter

    Confused

    Nice of them to give me the wrong one on Friday

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •