Question about a stepdown transformer
Hello,
I am looking to find the rated amps for the sencondary of a stepdown transformer. Three phase primary is 460/575V, secondary 230V, 200VA. I am not sure if I should calculate the secondary side of the transformer as 3 phase or single since it is only 2 wires coming out of the secondary.
Calculations:
3 phase- 200/230/1.73= .5 Amps
Single Phase- 200/230= .87 Amps
I am not sure which is correct and I could really use the help thanks.
-
02-10-2011, 07:19 PM #2
Professional Member
- Join Date
- Jul 2000
- Location
- Dallas,Texas
- Posts
- 4,804
There are no three phase transformers, just multple transformers placed together in a package.
In this case you have 1 transformer fed from 3 phase. However it is only tied to 2 of the 3 phases.
2 wires in 2 wires out, figure it as single phase.
IF this was a three phase transformer your calculation is incorect.
You have to allow for the 3 phases of power.
The equation is I = (KVA x 1000)/ (1.73 x E)
Assume this is a 20KVA 3 phase transformer instead of 200VA single phase.
(20 x 1000) / (1.73 x 230)
20000 / 397.9 = 50.26 ampsLast edited by wolfdog; 02-10-2011 at 07:36 PM.
-
02-10-2011, 07:26 PM #3
Regular Guest
- Join Date
- May 2010
- Posts
- 1,289
If it only has two wires coming out of the secondary it is single phase. I am not sure I understand you by saying, "There are no three phase transformers" when in fact there are? They are in delta or wye configurations
-
02-10-2011, 07:47 PM #4
New Guest
- Join Date
- Dec 2010
- Posts
- 4
Thanks for the help
-
02-10-2011, 08:16 PM #5
Professional Member
- Join Date
- Aug 2000
- Location
- Austell, Ga.
- Posts
- 1,246
The "Only" thing Wolfdog has been in error about is his chosing a puny 9mm against a full house 45ACP. His statement that there is no such thing as a 3ph. transformer is correct. Just because a 3ph transformer looks good on a schematic diagram, in all actuality it is nothing more than single phase transformers connected in Delta-Delta, Wye-Delta or Delta-Wye configuration.
Now....If I could only get da' Wolfdog seeing straight on the 9mm/45 issue all would be well.Ain't "None" of us as smart as "All" of us..
-
02-10-2011, 08:35 PM #6
Regular Guest
- Join Date
- May 2010
- Posts
- 1,289
I'd rather have a 9mm over a 45 as well, for many reasons. That is why I carry a 9mm and not a 45acp
-
02-10-2011, 10:21 PM #7
Professional Member
- Join Date
- Jul 2000
- Location
- Dallas,Texas
- Posts
- 4,804
I'm open to negotiation RichardL.
-
02-10-2011, 10:34 PM #8
don't forget wye-wye...but who would use those? stupid triplens!
as for the transformer...i do not believe that he has a 3 phase transformer PRIMARY and a single phase SECONDARY. my guess is that his transformer is a multi-tap PRIMARY transformer.
approximately 0.87 amps would be correct for 230 VAC, single phase.The weak aren't destroyed by the strong.
The weak are destroyed by the under-estimated.
I know a famous song that ends in 'my nose'. The artist is dead. Know who?
-
02-10-2011, 11:44 PM #9
Professional Member
- Join Date
- Jul 2000
- Location
- Dallas,Texas
- Posts
- 4,804
I don't believe I have ever met a Wye/Wye transformer configuration.
Delta/Delta for isolation and/or step down.
Delta/wye to produce a neutral and/or step down.
Wye/delta to step up.
The obvious question is Wye?
-
02-12-2011, 05:24 PM #10
Professional Member*
- Join Date
- Jun 2010
- Location
- Philadelphia PA
- Posts
- 2,139
Richardl both choices less than optimal
40 cal better ballistics and knockdown!If I could only get da' Wolfdog seeing straight on the 9mm/45 issue all would be well.You have got to learn from other people's mistakes! Because God knows you don't live long enough to make them all yourself !!!!!!!!


Reply With Quote