    Question about a stepdown transformer

    Hello,
    I am looking to find the rated amps for the sencondary of a stepdown transformer. Three phase primary is 460/575V, secondary 230V, 200VA. I am not sure if I should calculate the secondary side of the transformer as 3 phase or single since it is only 2 wires coming out of the secondary.
    Calculations:
    3 phase- 200/230/1.73= .5 Amps
    Single Phase- 200/230= .87 Amps

    I am not sure which is correct and I could really use the help thanks.

  2. #2
    Join Date
    Jul 2000
    Location
    Dallas,Texas
    Posts
    4,985
    There are no three phase transformers, just multple transformers placed together in a package.
    In this case you have 1 transformer fed from 3 phase. However it is only tied to 2 of the 3 phases.
    2 wires in 2 wires out, figure it as single phase.

    IF this was a three phase transformer your calculation is incorect.

    You have to allow for the 3 phases of power.

    The equation is I = (KVA x 1000)/ (1.73 x E)

    Assume this is a 20KVA 3 phase transformer instead of 200VA single phase.

    (20 x 1000) / (1.73 x 230)

    20000 / 397.9 = 50.26 amps
    Last edited by wolfdog; 02-10-2011 at 08:36 PM.

  3. #3
    Join Date
    May 2010
    Posts
    1,295
    If it only has two wires coming out of the secondary it is single phase. I am not sure I understand you by saying, "There are no three phase transformers" when in fact there are? They are in delta or wye configurations

  4. #4
    Thanks for the help

  5. #5
    Join Date
    Aug 2000
    Location
    Austell, Ga.
    Posts
    1,296
    The "Only" thing Wolfdog has been in error about is his chosing a puny 9mm against a full house 45ACP. His statement that there is no such thing as a 3ph. transformer is correct. Just because a 3ph transformer looks good on a schematic diagram, in all actuality it is nothing more than single phase transformers connected in Delta-Delta, Wye-Delta or Delta-Wye configuration.
    Now....If I could only get da' Wolfdog seeing straight on the 9mm/45 issue all would be well.
    Ain't "None" of us as smart as "All" of us..

  6. #6
    Join Date
    May 2010
    Posts
    1,295
    I'd rather have a 9mm over a 45 as well, for many reasons. That is why I carry a 9mm and not a 45acp

  7. #7
    Join Date
    Jul 2000
    Location
    Dallas,Texas
    Posts
    4,985
    I'm open to negotiation RichardL.

  8. #8
    Join Date
    Aug 2006
    Location
    Mixing oil and fire with a big spoon.
    Posts
    4,530
    Quote Originally Posted by RichardL View Post
    The "Only" thing Wolfdog has been in error about is his chosing a puny 9mm against a full house 45ACP. His statement that there is no such thing as a 3ph. transformer is correct. Just because a 3ph transformer looks good on a schematic diagram, in all actuality it is nothing more than single phase transformers connected in Delta-Delta, Wye-Delta or Delta-Wye configuration.
    Now....If I could only get da' Wolfdog seeing straight on the 9mm/45 issue all would be well.
    don't forget wye-wye...but who would use those? stupid triplens!

    as for the transformer...i do not believe that he has a 3 phase transformer PRIMARY and a single phase SECONDARY. my guess is that his transformer is a multi-tap PRIMARY transformer.

    approximately 0.87 amps would be correct for 230 VAC, single phase.
    "If you pull one more stunt like you just pulled with Tommy, you won't have to get on a plane because I will personally kick your ass from here to Korea!" - Best of the Best

  9. #9
    Join Date
    Jul 2000
    Location
    Dallas,Texas
    Posts
    4,985
    I don't believe I have ever met a Wye/Wye transformer configuration.
    Delta/Delta for isolation and/or step down.
    Delta/wye to produce a neutral and/or step down.
    Wye/delta to step up.

    The obvious question is Wye?

  10. #10
    Join Date
    Jun 2010
    Location
    Philadelphia PA
    Posts
    2,198

    Richardl both choices less than optimal

    If I could only get da' Wolfdog seeing straight on the 9mm/45 issue all would be well.
    40 cal better ballistics and knockdown!
    You have got to learn from other people's mistakes! Because God knows you don't live long enough to make them all yourself !!!!!!!!