Results 1 to 6 of 6
  1. #1
    Join Date
    Apr 2005
    Posts
    333
    Post Likes
    What's the minimum outdoor air temp you would recommend checking the AC. I've typically known it to be about 70. If its colder outside, has anyone ever wrapped plastic around the cond coil to raise head pressure to read your gages. This is something I've been TOLD to do where I'm working, but I really question it!
    meanwhile, back at the ranch.....

  2. #2
    Join Date
    Feb 2004
    Posts
    2,584
    Post Likes
    what temp. are you going to simulate by wrapping the condenser (or disconnecting the ofm). that is an unknown, so you will not know if pressures/temps are correct.

    minimum of 65 degs. 90 better.

  3. #3
    Join Date
    Nov 2000
    Location
    Upstate, SC
    Posts
    3,058
    Post Likes
    Age old question...lol. I have read manufactures data recommending putting plastic around the coil to get the condensing temp up to 90º F, so it is plausible to do from time to time. I have done it myself a few times, but I wouldn't make it a habit. In all honesty, sometimes you just have to do what you have to do to complete the call and none of us can control the weather.

    Bobby

  4. #4
    Join Date
    Sep 2004
    Location
    Glendale AZ
    Posts
    299
    Post Likes
    When possible, cross check using at least 2 methods. Start with a charging chart in the unit. It has its limitations though, if your air flow is less than 400 CFM per ton(most are ) and your line set is different than listed, these can effect the charts accuracy. Next, look at superheat and subcool. If your super heat is high, you would also expect your subcool to be high.(the outdoor coil storing refriderent). The superheat may be high when the ambiant is low. The cooler outdoor temerature results in lower operating pressures. The lower the liquid line pressure, the less refridernt the indoor metoring device can move. If you have subcool of 15-20 degrees, you have plent of charge in the unit. If your superheat is also high (20-30 degrees)try driving up the dicharge pressure(disconect outdoor fan ) and watch your superheat come down, as the indoor metoring device starts moving more refridgerent.
    (Thats from Dayrl)

    [Edited by danj on 04-27-2005 at 11:23 PM]
    The bitterness of poor quality remains long after the sweetness of low price has gone.

  5. #5
    Join Date
    Apr 2005
    Posts
    333
    Post Likes
    Thread Starter
    Thanks for the info!
    meanwhile, back at the ranch.....

  6. #6
    Join Date
    Nov 2004
    Posts
    84
    Post Likes
    TO BE SURE I weigh in the charge so i won't have to come back in warm weather

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Related Forums

Plumbing Talks | Contractor MagazineThe place where Electrical professionals meet.