    Leaks on a York YS chiller

    I have some leaks on a YSCBCAS1CGA with a YCCH163L0129YB compressor. One is on the slide valve housing to compressor and the second one is on the next piece in on the compressor. I have tried all my contacts and haven't found out if this can be done in the field or not. Does anyone know and if it can be done I guess I'm looking for the Frick YCCH163 manual. Iv'e got one for the TDSH163 but I don't know if there the same.

  2. #2
    Join Date
    Jan 2009
    Location
    Florida
    Posts
    210
    Post Likes
    what you have is a DXS compressor

  3. #3
    Join Date
    Mar 2005
    Location
    Indiana
    Posts
    459
    Post Likes
    Thread Starter
    That looks like the air cooled compressor. This is a water cooled unit, appr. 250 tons.

  4. #4
    Join Date
    Mar 2005
    Location
    Indiana
    Posts
    459
    Post Likes
    Thread Starter
    This is a drawing of the compressor from the IOM.
    Attached Thumbnails Attached Thumbnails York screw 001.jpg  

  5. #5
    Join Date
    Jul 2006
    Location
    The Great country of Texas
    Posts
    429
    Post Likes
    Quote Originally Posted by DFZ View Post
    what you have is a DXS compressor
    Its not a DXS it is the 163 mm upside down Frick screw.
    "I'm from Texas, what country are you from?"

  6. #6
    Join Date
    Mar 2005
    Location
    Indiana
    Posts
    459
    Post Likes
    Thread Starter
    Ive got to take all the gas out anyway to repair other leaks, I would like to repair all the leaks even though the two on the compressor are small. Doesn't anyone have any more info on the Frick compressor?

  7. #7
    Join Date
    Dec 2008
    Location
    Dixiana, AL
    Posts
    2,625
    Post Likes
    The O ring can be replaced on the compressor end of the hydraulic cylinder. The other section is starting to get into the compressor itself and you'll have to release the slide valve spring to get at it, so it's probably not a good idea. Not to say that you can't, just probably not a good idea.

  8. #8
    Join Date
    Jan 2009
    Location
    Florida
    Posts
    210
    Post Likes
    sorry my bad.

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •