Can anyone tell me EXACTLY how the reset dial and return air sensor operates on a W7100 cooling only discharge air set up?
Dis spt 55F
Reset pot 70F
Band 10F
Two stage unit cool only

PS I understand how warm up and heat work, Can you tell me Eaxctly how much reset above the discharge 55F setpoint I will have with the above settings? I have been told thet you divide 3 into the band , so that would give me 3.33F set up per degree over the reset 70F setting???