    Aux heat problem

    I have a EWC BMPlus 3000 rev B Ultra Zone Control system with a Comfort Aire 2 stage Geothermal. My problem is my electric bill is way high. I was told by the tech that my control panel will light Y1 when 1st stage heating is being used and Y2 when the 2nd stage is being used, then finally EM when emergency heat is needed. My system is going from Y1 then straight to Emergency heat after about 30 minutes. Is there anything I can do to fix this?


    I have turned off my emergency heat breaker, is that ok?

  2. #2
    Join Date
    May 2005
    Posts
    161
    Post Likes
    My thermostat distinguishes between aux heat and emergency heat. Emergency heat is only the backup electric elements while the aux heat is both. You might want to check and see what is actually going on. I think emergency is activated when it thinks the compressors aren't working at all.

  3. #3
    Join Date
    Nov 2006
    Location
    TEXAS
    Posts
    806
    Post Likes
    Without seeing the system, it seems like a wiring issue with either the thermostat or zoning control. Best course of action is to have installing contractor come out and verify the aux. strips are not coming on with the second stage heat.
    Avatar is a tribute to my Great Grandfather, Andrew Stewart. This pin was one of his advertisements for his heating and plumbing business. I never knew him but must of inherited his love of things mechanical since I am the only blue collar worker in the family

  4. #4
    Join Date
    May 2011
    Location
    Massachusetts
    Posts
    4
    Post Likes
    Not sure if you got the problem fixed or not - but I thought I would reply anyway. I have seen this problem before. It was a bad thermostat. Swap the thermostat out and see if that helps.

  5. #5
    Join Date
    Oct 2009
    Location
    new jersey
    Posts
    621
    Post Likes
    We use thermostats that can delay the electric heater uptown 120 min. Also w/ outdoor sensor can stop heater according to outdoor temp. We set it below 20 deg.

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •