how to fix over sized unit with banging customer
I responded to a call where the evaporator and the condenser the evap is 3 tons and the condenser is 5 ton how can I correct this problem with out changing what's there and costing the owner crazy money.
I have three years in the trade one in school. Mostly walk ins and reach in units in time
The three ton unit. Have a txv for three ton. As well would a bigger txv hurt or just flood the evaporator. Or could I add a nother evap on to take away some refrigerant from the other but keep the regular condenser.
-
02-07-2011, 11:26 PM #2
Is it actually causing a problem? I'm thinking an oversized condenser shouldn't really be a problem.. Perhaps you may have to get more water flow through it, but I'd doubt even that.
-
02-08-2011, 05:05 PM #3
Professional Member
- Join Date
- Mar 2003
- Posts
- 7,249
compressor is probably moving more gas out of the evap than necessary, causing low pressure condition in low load? there are ways to skin that cat none of which is easy.
-
02-08-2011, 05:11 PM #4
Regular Guest
- Join Date
- Mar 2008
- Posts
- 6
Hot Gas by-pass valve with 3ton txv
-
02-08-2011, 05:32 PM #5
Professional Member
- Join Date
- Sep 2005
- Location
- Texas
- Posts
- 2,793
If you polish a turd, at the end of the day you end up with a polished turd
...do it right
-
02-08-2011, 10:21 PM #6
Professional Member*
- Join Date
- Dec 2005
- Posts
- 1,655
If the building load is 3 tons then change OD unit to 3 tons.
If building load is 5 tons then make sure the ducts can handler at least 1800 CFM, and power is large enough, then change the ID unit to 5 tons.
If the owner said he does not want to change any equipment, then tell him "I ain't no miracle worker and good luck"
-
02-08-2011, 11:45 PM #7
Professional Member
- Join Date
- Nov 2004
- Location
- Oxnard, CA
- Posts
- 35
The problem with the "marriage" of a 5T compressor to a 3T evaporator is that the evap cannot produce as much vapor as the compressor can pull, resulting in a lower-than-normal suction temp. A compressor operating at a low suction pressure will consume more kw/ton. If the mis-match is severe, the suction pressure can be so that the saturation temp that corresponds to the evap pressure is below freezing, which can cause the condensate on the evap to freeze up, blocking airflow completely. You can fix that problem by installing an EPR (evaporator pressure regulator) between the evap and the compressor. It will sense the upstream pressure, and modulate closed (creating a pressure drop) to prevent the evap from getting below freezing temp. But you will still be stuck with an inefficient compressor because of the low suction pressure after the EPR.
-
02-09-2011, 07:44 PM #8
So which is sized improperly the evap or the condenser?
Who makes the equipment?
How many cfm's are you moving? Fan in evap set to hi.
If the evap is the correct size and the condenser is the improperly sized component I would pick up the extra sub-cooling/ efficiency and install a smaller compressor in the existing condensing unit.It takes courage to grow up and turn out to be who you really are.
- E.E. Cummings
-
02-09-2011, 08:48 PM #9
Professional Member
- Join Date
- Apr 2007
- Location
- Pa
- Posts
- 738
Sometimes this is done on purpose i.e. dehumidification. What is the reason you got called to the job? What part of the country do you live in? 5 ton with a 3 ton is a bit different compared to what I have run across.
-
02-10-2011, 12:18 AM #10
Professional Member
- Join Date
- Jul 2010
- Location
- Edmonton
- Posts
- 90
Measure pressure drop across and entering liquid temp of the TXV. Work backwards from there to size a TXV for 3 ton capacity.
You can also bring up the liquid temp entering TXV to decrease capacity. Sometimes that's insulating the liquid line, sometimes it involves blocking off some of the condenser.
HTHI came upon this pile of junk, the torch has been passed. I take ownership of things shaped before me, it is now my responsibility.
But what are you suppose to do when you see yourself in that pile of junk?
-
02-10-2011, 09:01 AM #11
Regular Guest
- Join Date
- May 2008
- Posts
- 6
-
02-10-2011, 10:14 AM #12
Removed by Admin- No Return
- Join Date
- Aug 2009
- Posts
- 2,459
Technically I don't see why an oversized condenser is all that terrible.
As long as the compressor, evaporator and TXV all match, the oversized condenser is simply going to be able to shed more heat more easily or at a lower fan speed. You will of course need more refrigerant to fill the larger circuit but in the end you could probably run the condenser fans at a lower speed thus reducing both noise and cost.
What type of compressor(s) are involved? Any issues with keeping enough oil in the system?
-