    TO Professional folks:

    I need your help on determining what me and the other tech did wrong!

    5ton Heatpump outside unit was working and about 12 years old. we replaced about 3ft of low & high pressure line outside that goes to the heatpump. vaccum the system and tried to fill it up with R22. place the termostat on cool and turn it on. we had to kick start the switch on the heatpump, but the Low pressure gauge goes to high (clockwise) and the high pressure guage goes to zero(counter clockwise) the we have to stopped the procedure becuse the compressor and the low pressure line gets very hot.

    Note: we did not do anything with the wireing. and want to understand what has happend? would you advise if you know what is happening?

    I believe some how this has stock in heat mode! is it?

    Thanks in advance for your help.

    Mark

  2. #2
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    68,563
    Did you melt any of the stat wire going to the unit.

    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  3. #3
    Join Date
    Feb 2005
    Location
    Alabama
    Posts
    534
    Almost sounds like the system is running in Heatpump instead of AC with the service valves closed.
    "If you can't fix it, don't break it."

  4. #4
    Join Date
    Apr 2004
    Posts
    11

    heatpump Goodman

    No wires have been melted and everything is in a good shape except I am not sure how to get it out of the heat mode. is there any idea? Could there be a block in the system? how about the reverse valve?

    any bright idea, instead of insults?

    Thanks for your professional ideas?

    Mark

  5. #5
    Join Date
    Nov 2000
    Location
    Eastern PA
    Posts
    68,962
    Let me guess; the indoor unit is Rheem or Ruud air handler?
    Government is a disease...
    ...masquerading as its own cure…
    Ecclesiastes 10:2 NIV


  6. #6
    Join Date
    Apr 2004
    Posts
    11

    goodman heatpump

    no the unit inside is Heil airhandler (gas furnice + air handler New))? what difference would it make? Please specify?


  7. #7
    Join Date
    Nov 2000
    Location
    Eastern PA
    Posts
    68,962
    You need to make sure that the unit has 24v between the orange and the blue wires at the heat pump. Rheem systems do not energize orange.

    Why in the world did you put a new heat pump onto an old system?
    Government is a disease...
    ...masquerading as its own cure…
    Ecclesiastes 10:2 NIV


  8. #8
    Join Date
    Apr 2004
    Posts
    11

    goodman heatpump

    the blue wire and the orange that come from the termostat?
    is that what you are saying?

    Thanks

  9. #9
    Join Date
    Nov 2000
    Location
    Eastern PA
    Posts
    68,962
    No, the blue wire and the orange wire at the heat pump must have 24 volts in the cooling mode.
    Government is a disease...
    ...masquerading as its own cure…
    Ecclesiastes 10:2 NIV


  10. #10
    Join Date
    Apr 2003
    Location
    Eugene, Oregon
    Posts
    1,209
    Originally posted by mark01
    TO Professional folks:

    I need your help on determining what me and the other tech did wrong!

    5ton Heatpump outside unit was working and about 12 years old. we replaced about 3ft of low & high pressure line outside that goes to the heatpump. vaccum the system and tried to fill it up with R22. place the termostat on cool and turn it on. we had to kick start the switch on the heatpump, but the Low pressure gauge goes to high (clockwise) and the high pressure guage goes to zero(counter clockwise) the we have to stopped the procedure becuse the compressor and the low pressure line gets very hot.

    Note: we did not do anything with the wireing. and want to understand what has happend? would you advise if you know what is happening?

    I believe some how this has stock in heat mode! is it?

    Thanks in advance for your help.

    Mark
    Did you replace the heat pump? By your post it would appear that you moved it or ???
    If your suction line is hot and reading high pressure it is in the heat mode. Most Heat pumps have a third access port that shows true suction, it is located on the bulk head above the line set service ports. Blue should go there and red on the large line for reading pressures in the heat mode. If you are trying to cool and get heat your O/B terminals may be reversed, or set up with the t-stat is wrong. Just guessing here, good luck
    Proud supporter of Springfield Millers and Oregon Ducks.

  11. #11
    Join Date
    Apr 2005
    Location
    Richmond, Virginia
    Posts
    365
    I've had the same problem, the reversing valve doesn't reverse. It's normal position is in "heat" mode. I would try the following.

    With the outdoor unit off and power to the indoor unit (you need the 24 V circuit to be live) "bump" the reversing valve by pulling one of the wires which control the reversing valve off the contactor and putting it back on. This is also an indication your contactor is going back - check for pitting, loose wire one coil, etc.

    Double check your voltages on the 24 V circuit.

    Hope this helps.

    Sean
    Sean Cantrell

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event