  1. #14
    Join Date
    Apr 2004
    Posts
    7,680
    I think Mark made the wise comment. Look at the gauges the operating pressures are very low on the scale for R-22 and difficult at best to be accurately read. many of the R-410A gauges have 20 PSIG marks on the high side. That leaves an awful large interperatation when looking at R-22 saturation temps. The other kicker may be oil but worse yet refrigerant. Your gauges always have refrigerant in them, they will purge for 20 minutes when disconnected. Why subject your equipment to that?

    Get a set for each and be done with it.

  2. #15
    Join Date
    Jun 2001
    Location
    Louisville, KY
    Posts
    12,150
    Originally posted by docholiday
    Look at the gauges the operating pressures are very low on the scale for R-22 and difficult at best to be accurately read. many of the R-410A gauges have 20 PSIG marks on the high side. That leaves an awful large interperatation when looking at R-22 saturation temps.
    That's my concern with it. Gauges are most accurate in 25-75% of full scale. You'll be pushing the lower end of that range on a R-22 system.