    Oct 2001
    Hmm
    if you ever been to the GARDEN and the old Beefsteak Charlie as you walk in off 7TH Avenue,it is an RTAA140 installed 7 years ago and is flat(both CKTs 260 LBS total) and sitting thru 7 winters since.it is 460V across the line on 2-70 ton hellicals with 10 condenser fans{non-vfd)with the old UCP-1 control module.it going to be turned into a Borders Bookstore with the second floor included,chiller/and pumps are on the 3rd floor walk out(above that glassed in area between MSG and 2 Penn Plaza).dryers,oil and filters,freon,vac test.....etc the usual,reads 100,000 OHMS to ground on all loads.any things that the compressor might do after sitting for at least 5 years with no gas,the condenser fans are a definite especially at 460V to blow up on start or on counter-rotation starts!
    "when in doubt...jump it out" http://www.youtube.com/watch?v=U1qEZHhJubY
    Oct 2001
    coils inside and out are as shipped,minimal dirt if any
    Oct 2001
    main entrance to the right all new chilled water AHUs and controls...."installed by others" as the prints always say.