    Jul 2002
    NorthEast
    Heat Timer Gold Short cycles
    Sometimes The outdoor temperature reading keeps keeps bouncing up and down
    within one degree of the setpoint call for heat.
    The outdoor air temperature will equal the setpoint temperature for a a few seconds.
    The boiler will begin its purge cycle.
    Suddenly the outdoor air temperature will go one degree or two above the setpoint.
    The boiler will then shut down.
    The outdoor air Temp will then drop about a degree below setpoint.
    Once again the boiler starts its purge cyccle
    This happens at about a 37 degrees O.A.Temp .
    The setpoint is 36 degrees.
    Is there any way to dampen the Heat Timer Response
    The outoor air sensor appears to be accurate.
    Jan 2011
    London, England
    More details needed about controls system fitted.
    Mount Airy, MD
    "If" you're talking about what I think you're talking about then you might have better luck in the boiler "PRO" section of the site.
    I am pretty certain that I no longer have the info on that POS reset/staging control.
    Cleancondeser you need to go PRO !!!
    Moving your question to commercial
    Jul 2001
    Canada
    The info for the so called POS is still aavailable http://www.heat-timer.com/en/ProductDetail.aspx?Id=29
    you should be able to adjust that to a certain degree, but will need the manual and some thought process to do so.