    how to remedy ice on goodman hp

    does anyone have any suggestions about how to remedy goodman hps that have a 2-4 inch band of ice that will not go away around bottom of outdoor coil confirmed charge defrost board and stat also replaced rv on some that they had recalled but problem still persists on mutiple gsz13024 and 30s thanks for the help

  2. #2
    Get the unit up a little bit off the pad, make sure the drain holes are cleared, and make sure the defrost stat is on the affected coils.

  3. #3
    Join Date
    Oct 2003
    Location
    Washington
    Posts
    7,405
    Quote Originally Posted by tlb View Post
    does anyone have any suggestions about how to remedy goodman hps that have a 2-4 inch band of ice that will not go away around bottom of outdoor coil confirmed charge defrost board and stat also replaced rv on some that they had recalled but problem still persists on mutiple gsz13024 and 30s thanks for the help

    Apply a mister to the entire unit so the ice is more uniform. j/k


    If it is a demand defrost, make sure your sensors are attached and reading properly. I've had some issues with the coil sensors within the last few months as the clamps aren't the finest.

  4. #4
    Join Date
    Jan 2011
    Location
    TN
    Posts
    93
    these units use time and temp defrost not demand the have snap type tsat no sensors have considered installing stat with higher termination temp on these units good idea or bad idea

  5. #5
    Join Date
    Oct 2003
    Location
    Washington
    Posts
    7,405
    Quote Originally Posted by tlb View Post
    these units use time and temp defrost not demand the have snap type tsat no sensors

    Add a demand defrost system to it then.

  6. #6
    Join Date
    Jan 2011
    Location
    TN
    Posts
    93
    how would this help by holding the defrost cycle in longer

  7. #7
    Join Date
    Sep 2009
    Posts
    382
    Goodman has a service bulletin on this particular issue, 2t-2.5t HPs. The remedy is to relocate the defrost temp-rise cutoff sensor to a lower position. Go to your supply house to look it up.


    Quote Originally Posted by tlb View Post
    does anyone have any suggestions about how to remedy goodman hps that have a 2-4 inch band of ice that will not go away around bottom of outdoor coil confirmed charge defrost board and stat also replaced rv on some that they had recalled but problem still persists on mutiple gsz13024 and 30s thanks for the help