Results 1 to 9 of 9

Thread: train heat pump

  1. #1
    Join Date
    Nov 2004
    Posts
    4
    Post Likes

    Hmm

    I have a train heat pump model# TWNO42C100, last year I replaced compressor due to a locked rotor. Now Im replacing it again due to a dead short. Does anyone know if this model had problems with compressors or if there is something may be overlooking ? Thanks for any advise.

    Chuck

  2. #2
    Join Date
    Apr 2003
    Location
    Eugene, Oregon
    Posts
    1,210
    Post Likes
    I would check for voltage drop on start up. You may need a hard start kit.
    Proud supporter of Springfield Millers and Oregon Ducks.

  3. #3
    Join Date
    Jul 2002
    Location
    Zelienople, Pa
    Posts
    2,965
    Post Likes
    Originally posted by chuck29
    I have a train heat pump model# TWNO42C100, last year I replaced compressor due to a locked rotor. Now Im replacing it again due to a dead short. Does anyone know if this model had problems with compressors or if there is something may be overlooking ? Thanks for any advise.

    Chuck
    You're overlooking a qualified contractor.

    Is the coil an ARI rated match?
    Did he put a filter drier on?
    Did he even pull a vacuum?
    How tall are you Private???!!!!

  4. #4
    Join Date
    Aug 2004
    Location
    North Richland Hills, Texas
    Posts
    15,621
    Post Likes
    Something is wrong with the system that is causing the compressor failures. Trane compressors are some of the most reliable there are.

    Out of curiosity, how was it determined that the compressor is shorted to ground?
    I have run many 2nd opinion calls for shorted compressors on Trane systems and most of the time find that it is the crankcase heater shorted out, nothing wrong with the compressor.
    A lot of people seem to be to lazy to actually remove the leads from the compressor and check at the compressor terminals. If anyone ever tells you your compressor is shorted to ground, and they are not checking at the terminals on the side of the compressor, don't trust them.

  5. #5
    Join Date
    Mar 2002
    Location
    Richmond, Virginia
    Posts
    4,262
    Post Likes
    It definately sounds like something is up with your TRANE heat pump. Have them check all the particulars to try and determine what is causing the premature failures.
    There is nothing more frightful than ignorance in action....Mark Twain

  6. #6
    Join Date
    Apr 2004
    Location
    Niantic, Illinois
    Posts
    545
    Post Likes
    Was this a matched system when installed? The indoor and outdoor section of system with new linesets? Trane rarely has problems like this without major contractor error.

  7. #7
    Join Date
    Apr 2003
    Location
    Iowa
    Posts
    763
    Post Likes
    high side burnouts should, when replacing the compressor it is advised nowadays to change the inside coil and the lineset and definately change the filter inside the unit. Some think that nitrogen can blow out the lines good enough but it still leaves acid and carbon in the lines.... hard to blow thru oil. Anyway you will see a compressor fail in a year pretty often if you don't change them.

  8. #8
    Join Date
    Mar 2005
    Location
    leland nc
    Posts
    4,526
    Post Likes
    it is hard to stop a train
    if you dont know what your doing you have a train reck
    i recomand you find a new contractor and get a second opinion. something is not right with your system if you went through two train compressors in less then a year or someone does not know what he is doing and should go back to school before touching someone esles unit
    call train and see if they can recomend a contractor for you and put a stop to this train reck

  9. #9
    Join Date
    Mar 2003
    Posts
    1,877
    Post Likes
    compressor failures are due to overcharging of refrigerant,
    dirty evap coils, low return air, oversized metering devises and restrictions.