Where can I find this?
Anyone know where I can find an actuator for the low ambient dampers on an old Trane CGAE-C40. The Robert Shaw model number is P020-2202?
Here is a link to a cut sheet.
http://www.icca.invensys.com/UNILINE/d/d109.pdf
I got it from a google search, but I haven't found a place to order one.
The Robert Shaw number crosses to a Uni-Line order number 3520-022
-
02-03-2011, 05:35 PM #2
Regular Guest
- Join Date
- Dec 2010
- Posts
- 20
-
02-03-2011, 07:09 PM #3
Trane recommends changing it to an electric actuator. You have to add a sat. cond. temp. sensor and the module I think. I believe it's pretty expensive though. I found a similar actuator but the stroke was like an inch shorter, if I remember correctly, but I made it work. I don't think you can find that actuator any more.
-
02-03-2011, 07:40 PM #4
Professional Member
- Join Date
- Jun 2003
- Location
- in a tree looking in your window
- Posts
- 1,101
there is one on ebay for about 350.00
If you dont stand behind our troops, please feel free...........to stand in front of them.
-
02-03-2011, 08:05 PM #5
Why oh why not go with vfd
It takes courage to grow up and turn out to be who you really are.
- E.E. Cummings
-
02-03-2011, 10:05 PM #6
Regular Guest
- Join Date
- Jul 2010
- Posts
- 36
The Trane Parts Center quoted me @ $4000 for the parts to retrofit. The parts included KIT03939 and KIT03942. They say that everything I would need is in these kits.
Add markup and labor and you are probably talking about a $10,000 retrofit.
The chiller is a 1995 model, and is about worn out. If I was the customer I would not put that kind of money into it.
-
02-03-2011, 10:09 PM #7
Regular Guest
- Join Date
- Jul 2010
- Posts
- 36
-
02-03-2011, 11:28 PM #8
Jack the dampers open and put a Penn press. switch on that fan.
-
02-04-2011, 07:57 AM #9
Regular Guest
- Join Date
- Jul 2010
- Posts
- 36
That's how it is now. I get LPC trips when it's really cold. The "on/off" control of the fan seems like it's causing me problems. It seems like the TXV can't respond fast enough to the rapid changes in head pressure and my low pressure takes a nose dive when the fan cycles on.
LWT setpoint is 40 degF.
-
02-04-2011, 06:23 PM #10
-
02-04-2011, 06:48 PM #11
Since you said it has a TXV you might consider installing a Johnson Controls A350 and a 24v/0-10 actuator on the existing dampers. Strap the sensor that comes with the controller on the liquid line and set the controller to your desired liquid temp.
I think the price would be reasonable and you have power for the controller readily availible. You would have to make a weathersheild for the actuator.I'm good at making things cold...You can ask my first two wives!
-
02-04-2011, 07:26 PM #12
Professional Member*
- Join Date
- Jan 2008
- Location
- Dallas ,Texas
- Posts
- 3,512
-
02-04-2011, 07:28 PM #13
Professional Member*
- Join Date
- Jan 2008
- Location
- Dallas ,Texas
- Posts
- 3,512


Reply With Quote