    Currently doing some research on the *new* Belimo PICCV valves.
    Has anyone ever used them yet, and have any stories (good or bad) to tell?


    Cheers.

  2. #2
    Join Date
    Oct 2003
    Location
    Minnesota
    Posts
    1,382
    Originally posted by lurner
    Currently doing some research on the *new* Belimo PICCV valves.
    Has anyone ever used them yet, and have any stories (good or bad) to tell?


    Cheers.
    No stories. We Installed around 34 in each of two buildings on the air handlers. <Shrug> No compaints, seem to be working as advertised. Been online for almost a year now.

  3. #3
    Join Date
    Apr 2005
    Posts
    104

    Hmm

    Regarding your installation, did you still wind up using balancing valves as well as the PICCV valves for each coil?

  4. #4
    Join Date
    Oct 2003
    Location
    Minnesota
    Posts
    1,382
    Originally posted by lurner
    Regarding your installation, did you still wind up using balancing valves as well as the PICCV valves for each coil?
    Nope. Tho the water circulation is on a VFD system. So we did install DP sensors at the farthest (last valve) to ensure it had the minimum pressure necessary.

  5. #5
    Join Date
    Apr 2005
    Posts
    104
    Great, thanks!