Results 1 to 6 of 6

Thread: Heat Pump

  1. #1
    Join Date
    Apr 2005
    Posts
    1
    Post Likes
    Can You wire a low voltage side of a Heat Pump( Single Stage) with only 3 wire?

  2. #2
    Join Date
    Nov 2000
    Location
    Eastern PA
    Posts
    69,126
    Post Likes
    Sure. Somethings not going to operate, but what the hay!
    Government is a disease...
    ...masquerading as its own cure…
    Ecclesiastes 10:2 NIV


  3. #3
    Join Date
    Apr 2005
    Posts
    2
    Post Likes
    You can wire a heat pump with 3 wires to either heat or cool, but not at the same time. If you wired it to cool in the summer you would have to rewire it in the winter to make it heat. With only 3 wires you would not have a defrost in the winter time nor any monitoring controls.

  4. #4
    Join Date
    Mar 2002
    Location
    Richmond, Virginia
    Posts
    4,264
    Post Likes
    Why would you want to? There are remedies for situations like that.
    There is nothing more frightful than ignorance in action....Mark Twain

  5. #5
    Join Date
    Jun 2003
    Location
    Florida
    Posts
    9,546
    Post Likes
    Using relays,you could make it work with only 3 wires (cool,heat),but your e-heat would either be on all the time or off all the time if the 3rd wire is common.
    If everything was always done "by the book"....the book would never change.

  6. #6
    Join Date
    Nov 2000
    Location
    Eastern PA
    Posts
    69,126
    Post Likes
    OK, "IF" your heat pump has a defrost board that does require being energized all the time, you can get away with wiring just the contactor hot lead, the reversing valve hot lead and the common.

    With that configuration, only "IF" a continuous hot lead is "NOT" required by the defrost control, your heat pump will operate both heating and cooling but will not energize the aux. heaters during defrost.

    Now..."IF" your heat pump happens to be a Rheem/Ruud product that requires constant energizing of the defrost board, you can also jumper the reversing valve control lead to the "hot" lead on the defrost board and it will still operate.
    Government is a disease...
    ...masquerading as its own cure…
    Ecclesiastes 10:2 NIV


Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Related Forums

Plumbing Talks | Contractor MagazineThe place where Electrical professionals meet.
Comfortech 365