    Quote Originally Posted by mryan1 View Post
    as long as the pump is the right size no need for a vfd on the loop
    Not if it's a variable-primary-flow (VPF) system.

  2. #28
    Join Date
    May 2008
    Location
    Central Pennsylvania
    Posts
    438
    Quote Originally Posted by jayguy View Post


    now THAT is funny!

    this chiller does not have 'softload'...at least not like it is applied to the other screw chiller products.

    Standard Ambient from the factory is 15F...Low Ambent Kit allows it to go to -10F. According to the model number, this unit is a Standard Ambient unit.

    attached is the closest i could get to swahili
    Thanks Jay, without looking it up I didnt realize the standard machine was good for down to 15 degrees. I wouldnt think that it would hit 15*F much in Florida, he should be good to go with that.

  3. #29
    Join Date
    Jan 2009
    Location
    Not in Iran
    Posts
    1,076
    Quote Originally Posted by emcontrols View Post
    You mentioned low evap alarm and other problems due to low ambient conditions. Do you really have isues or was this just a jab session??

    there are two types of transformers.,.,
    standard which has the 5-6 functions.,.,
    then the under and over from what i understand
    no signature blast'em man blast'em
    !!!KILL THE TERRORIST!!!

  4. #30
    Join Date
    Jan 2009
    Location
    Not in Iran
    Posts
    1,076
    Quote Originally Posted by Phisher View Post
    Not if it's a variable-primary-flow (VPF) system.


    no drive on the machine.,.,anyways going tomorrow

    going to check out compressor capacity , temp sensors, and inverter.,.,
    no signature blast'em man blast'em
    !!!KILL THE TERRORIST!!!

  5. #31
    Join Date
    Mar 2004
    Location
    ottawa canada
    Posts
    2,022
    NO! NO! NO!

    that is how the russian ones are fixed....geez....isn't anyone listening?


    Ok Im off to Siberia .......probably about the same temp there as here so I'll be right at home .

    graham, It's too cold in Canada for that Healey. I think it would be happier if it were parked farther south. I know a perfect garage in Va.


    Yep its cold but spring is coming and I can see the finish line for the car ......just in time .
    The 64 roars to life Whoo hoo ...shes a rolling chassis .
    You bend em" I"ll mend em" !!!!!!!
    I"m not a service tech.. I"m a thermodynamic transfer analyst & strategic system sustainability specialist
    Best Austin Healey In Show twice in 2013 .....All those hrs paid off .

  6. #32
    Join Date
    Mar 2004
    Location
    ottawa canada
    Posts
    2,022
    no drive on the machine going to check out compressor capacity , temp sensors, and inverter.,.,

    If theres no drive on the machine how are you going to check the inverter ?????


    Am i reading the wrong IOM again ????? Do i need the Chekoslovakian version

    JAAAAAYYYYYYY HEEEEEELLLLLP!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!! !!!
    The 64 roars to life Whoo hoo ...shes a rolling chassis .
    You bend em" I"ll mend em" !!!!!!!
    I"m not a service tech.. I"m a thermodynamic transfer analyst & strategic system sustainability specialist
    Best Austin Healey In Show twice in 2013 .....All those hrs paid off .

  7. #33
    Join Date
    Mar 2004
    Location
    ottawa canada
    Posts
    2,022
    here it is guyz
    Attached Files in chineese writing.pdf


    No wonder your having trouble fixin it .......thats the wrong manual ?????????????
    The 64 roars to life Whoo hoo ...shes a rolling chassis .
    You bend em" I"ll mend em" !!!!!!!
    I"m not a service tech.. I"m a thermodynamic transfer analyst & strategic system sustainability specialist
    Best Austin Healey In Show twice in 2013 .....All those hrs paid off .

  8. #34
    Join Date
    Aug 2006
    Location
    Mixing oil and fire with a big spoon.
    Posts
    4,267
    Quote Originally Posted by mlkwal1 View Post
    here it is guyz
    DON'T USE THAT CHINESE VERSION!!! there has been an upgraded IOM.

    for those that care, on page 8, center column, under bullet point #2 they say that the heaters are DE-ENERGIZED when the chiller is off. It was supposed to say that the heaters are ENERGIZED.

    at least that is how i read it.


    Quote Originally Posted by graham View Post
    ...Am i reading the wrong IOM again ????? Do i need the Chekoslovakian version...
    here you go (ends in CS)...and the norwegian one too with some of the longest words that i have ever seen!
    Attached Files Attached Files
    my 1st time jumping out of a plane...http://youtu.be/Kv38G0MHsGo

  9. #35
    Join Date
    Mar 2004
    Location
    ottawa canada
    Posts
    2,022
    Cant open the Nerwegian version Jay .....the words must be to big for this computer?????
    Do you have a Gaelic copy instead ?????
    The 64 roars to life Whoo hoo ...shes a rolling chassis .
    You bend em" I"ll mend em" !!!!!!!
    I"m not a service tech.. I"m a thermodynamic transfer analyst & strategic system sustainability specialist
    Best Austin Healey In Show twice in 2013 .....All those hrs paid off .

Page 3 of 3 FirstFirst 123

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event