    i am working with a
    rtaa 0804xl01a3dobp
    u00g02355
    working on and 80 ton air cooled trane., issue is that machine will trip on low evap temp and other diag due to cooler weather., what i would like to do is upgrade the ucp2 , not to a 530 , just add more ct's, if possiable, and be able to enable soft load., i have called the trane office, they are supposed to get back with me on this., any suggestions? can this be done?., i would think to upload software for what i am wanting to do..,
    no signature blast'em man blast'em
    !!!KILL THE TERRORIST!!!
    ottawa canada
    SAY WHAT ???????
    What do Ct's have to do with low evap temp ???????
    UCP 2 already has a soft load capability ( if you know how to use it )
    Aug 2010
    UK.
    As far as I am aware the Ucp on an RTAA is not upgradable like that. You could try low ambient mods like fitting condenser fan speed controllers.
    Not in Iran
    Quote Originally Posted by graham View Post
    SAY WHAT ???????
    i may have tried to explain alot in a little if that makes since.,., i was thinking to also add more ct's for unbalance , current ect.,.,
    what i am tring to do is to be able to enable soft load on ucp2., had another tech tell me that i need to go into service settings and play with low water temp, low refrig temp, and leave water temp., that the three of these combined and configured correctly that will help the nusince call.,
    now i can change the confiuration in those three to keep them as far apart,, but not freezing,, as possiable to avoid a call.,
    Not in Iran
    Quote Originally Posted by CoolFox View Post
    i was considering that as well., just didnt know what would be the most cost effective to customer to avoid the call he is worried about., actually , not very often does it really trip, however it does and thay dont want that.,
    ottawa canada
    The controller already has CT's so what will adding more do ????????
    You have a refrigerant temp issue and your leaping in with both feet to look for what ????
    Start at the beginning and look for the obvious problem first .
    Jun 2008
    This model should alreaady have low ambient fans, the fist 2 after the control cabinet, if not this is a good idea, under low ambient conditions this is your best bet
    Jun 2008
    Quote Originally Posted by mlkwal1 View Post
    i am working with a
    rtaa 0804xl01a3dobp
    u00g02355
    I'm just trying to figure out why your needing a software upgrade when there are other issues to address if your tripping low evap"meaning the weater temp is below 34 degrees for 300 seconds"
    May 2008
    Central Pennsylvania
    I know your in Florida so maybe you're machine is not equipt with the low ambient options. I would also guess that you are running straight water through the chiller and not glycol? The other tech is correct that the configuration can be changed but those settings are normally only changed if your running a glycol mix through the chiller, default settings are for water. Have you checked other possible issues like water flow and refrigerant charge? I'm sure if you post the full model number, one of the Trane guys on here will be able to tell you what the ODA temp design is for this chiller, I forget without looking it up. Good luck!
    Not in Iran
    Talking
    Quote Originally Posted by chillerguy81 View Post
    I know your in Florida so maybe you're machine is not equipt with the low ambient options. I would also guess that you are running straight water through the chiller and not glycol? The other tech is correct that the configuration can be changed but those settings are normally only changed if your running a glycol mix through the chiller, default settings are for water. Have you checked other possible issues like water flow and refrigerant charge? I'm sure if you post the full model number, one of the Trane guys on here will be able to tell you what the ODA design is for this chiller, I forget without looking it up. Good luck!
    that makes since., i am certain that does not have the soft load option ., i am familuar with the ucp 1 and 2., i have 2 rthc with the ucp2 controller and the option is enabled, not only that but its there!!!.,,. idk, that is why i was asking.,.
    and as far as the ct's ., i have read/seen somewhere that there were 2 sets of ct's on the power.,.,
    u say u know what i say.,.,usay??
    ottawa canada
    Jayguy..... where are you when we need you ???? Mlkwal is looking for a copy of the IOM for the 80/125 ton RTAA with UCP2 style controls ..........do you have a copy written in Swaahilli you could send him ????
    now THAT is funny!
    this chiller does not have 'softload'...at least not like it is applied to the other screw chiller products.
    Standard Ambient from the factory is 15F...Low Ambent Kit allows it to go to -10F. According to the model number, this unit is a Standard Ambient unit.
    attached is the closest i could get to swahili
    Not in Iran
    Quote Originally Posted by jayguy View Post
    now THAT is funny!
    nice