Thread: Velocity Pressure?
-
04-16-2005, 07:11 PM #1
Professional Member
- Join Date
- Nov 2004
- Location
- MA
- Posts
- 69
Has any one used the KMC SSS-1001 flow sensors to retrofit pressure dependent vavs to pressure independant. They come in three lengths dpending on the inlet size of the vav. Clearly this sensor is reading velocity pressure (diff pressure) as designd. My question is this... How does this sensor compare to the flow cross sensors that come standard with newer independent vavs? When I install a digital controller and read diff pressure will this be a usable input?
Thanks
I posted the above on another thread wtith 0 response. I hope this forum is the right one.
The existing vav's have tempmaster floating actuators. I hope to either install J/C VMA and use the diff pressuere sensor or keep the actuators in place and go with a VAV or UNT controler. I could use the diff (velocity) pressure and program hi/lo airflow limits.
What do think. Are there other options?
-
04-17-2005, 10:21 AM #2
Professional Member
- Join Date
- Feb 2005
- Posts
- 293
We've had good success using them on Honeywell smart actuators and Trane Retrofits Kits. There is always the need for calibration during setup. Its really the only option we've found. They main problem we've fouind is the hi pressure duct connection being incorrectly installed-not enough straight duct before the inlet of the VAV. I'd also like hear what others are using. Good Luck.
-
04-18-2005, 01:43 AM #3
Professional Member
- Join Date
- Dec 2004
- Location
- San Francisco Bay Area
- Posts
- 434
I've also had to use these SSS-100x flow sensors in retrofit situations where the factory flow sensors were broken over the years. By simply entering a valid k-factor into the DDC controller for the size of duct we're controlling, it works great.
-
04-18-2005, 07:17 AM #4
Professional Member
- Join Date
- Nov 2004
- Location
- MA
- Posts
- 69
That's good news. Thanks for the response.
Are there any good vav controlers out there that I could use with the exhisting floating actuator. I would need somthing stand alone that could be networked later.
Any sugustions?
-
04-19-2005, 01:29 PM #5
We've had very good luck with the SSS flow sensors - most of then are pretty close to being calibrated once you set up your box parameters. I've had a number of them that did not even need calibrating.
"How it can be considered "Open" is beyond me. Calling it "voyeur-ed" would be more accurate." pka LeroyMac, SkyIsBlue, fka Freddy-B, Mongo, IndyBlue