Results 14 to 20 of 20
    North St Paul MN
    I think Carrier had a problem a few years ago with their stats. Wondering if the Bryant stat is the same. If I recall, it had to have a resistor across R and Y? Or W and Y? I can't remember...
    I'd rather have a bottle in front of me, than a frontal lobotomy.
    Apr 2003
    Iowa
    your stat has a jumper from RC and RH doesn't it?
    Is the thermostat that was on there a power stealer type with no common?
    If so, there was a resistor you were suposed to install between C and W at the control board. Without the resister, power stealer thermostats can be flakey in the cooling mode on systems with a control board in the AH/furnace since there may not be a good low impedance electrical path from the W terminal on the control board through the controls to common. Power stealer thermostats have to "fake" a common to work. On a control board the 24v from the thermostat usually goes to a transistor on the board to "switch" the power on to a relay coil on the board, so there isn't a good electrical path for the thermostat to fake a common through..
    The odd thing is, sometimes you can have 2 units with the same board, and it will work fine on one but not the other...
    You also need the resistor on AS/Trane air handlers because there is NO electrical path to common from W until the fan relay closes.
    There generally isn't a problem in the heating mode since it can fake a common through Y, wich is always low impedance to common through the contactor coil in the outdoor unit.
    If you have a way to actually measure the impedance between W and common, generally if the impedance is over 25z, you need the resister, if it is below, you don't need it.
    I don't think I have ever seen a meter that can measure impedance that would be in a HVAC techs collection, so I follow a simple rule for power stealer thermostats.
    If W goes to a control board, or the air handler requires a call to G in the heating mode, install the resistor
    It scares me that I remember this crap....need a life.
    Central Kentucky
    Sounds like commitment to your profession.
    Keep the post coming they are great.
    Have you set up a Google alert for Carbon Monoxide yet?
    Click here to find out how.
    Dec 2001
    Woodstock Ga
    bryant stat used common to power up, W/R uses batteries this must be the difference
    i will go out there tomorrow, will post results
    mike
    In the land of the blind the one eyed man is King! semper fi
    North St Paul MN
    Yea, that's what I was thinking. Seems to me it's a 1K resistor if memory serves me right.
    Dec 2001
    Woodstock Ga
    common was used on all these stats, so resistor was not used.
    had one again, now 3 times. in every case, using a w/r fixed it, but builder demands bryant on every stat, unit, even humidifier.
    never saw this before, now 3 in 10 days. all of the other units in the 4 subdivisions are working like they should. we are pretty high volume, in my opinion (43 roughs on 2 system townhouses last week), so i see a variety of problems, but this is killin' me!