york YK MAXE centrifugal chiller
Results 1 to 13 of 13
  1. #1
    Join Date
    Jul 2010
    Location
    TN.
    Posts
    2

    york YK MAXE centrifugal chiller

    this chiller is a 134a system and is going out on excess surge. what is causing this machine to surge. the 134a system don't have a purge unit, the pressures don't never get below atmospheric pressure. and its making a loud noise at the condenser (rumbling noise). not used to working on a 134a machine so anyone have any suggestions? usually i would say it would be air in the system but like i said it keeps pos. pressure during the off cycle so air cant enter.

  2. #2
    Join Date
    Jun 2010
    Location
    U.A. (upper Alabama)
    Posts
    827
    Quote Originally Posted by supertech0971 View Post
    this chiller is a 134a system and is going out on excess surge. what is causing this machine to surge. the 134a system don't have a purge unit, the pressures don't never get below atmospheric pressure. and its making a loud noise at the condenser (rumbling noise). not used to working on a 134a machine so anyone have any suggestions? usually i would say it would be air in the system but like i said it keeps pos. pressure during the off cycle so air cant enter.
    Have you got design flow on cond. water and evap. water? Is there a possibility there's a strainer stopped up? What's you're small temp. diff. on both evap. and cond.?

  3. #3
    Join Date
    Jul 2010
    Location
    TN.
    Posts
    2
    well the design is good it has worked for several years now. i dont remember what the small temp difference was now sense im home! lol. i do know that the refrigerant pressures looked pretty good on the optiview control center. i dont really think that its a water problem it wasn't running high head pressure or nothing. if this machine wasnt a 134a system i would swear that it has air in the refrigerant and needs to be purged! first time i have ever seen a 134a chiller like this! but i will double check water just to make sure something aint just crazy there.

  4. #4
    Join Date
    Jun 2008
    Location
    Windsor, Ont.
    Posts
    480

    Question

    A lot more information would come in handy here, what are your entering and leaving water temps (evap and cond), what are your approach temperatures, just for a few basics. There are a lot of things that can cause surge or stall on any machine but it's impossible to diagnose without some numbers.

  5. #5
    Join Date
    Dec 2008
    Location
    Dixiana, AL
    Posts
    2,609
    You're going to have to get a lot more detailed than what you have. To ask what's causing a surge in a centrifugal chiller without giving a complete operating log is like asking everyone to hunt a needle in a haystack. You do say that design is good. So along with the operating log, it would help if you post the design data on the machine. We also need to know the machine setup.

    You also stated that it wasn't running high head pressure, but if it weren't a 134A machine you'd swear it had air in it. Air in a shell and tube condenser creates a high head condition no matter what type refrigerant you use. I believe it's safe to say that it may be in your best interest to get someone that's familiar with these type chillers to take a look at things.

  6. #6
    Join Date
    May 2001
    Location
    Western Wa
    Posts
    1,817
    Rapid dropping of the load?
    God Bless our Veterans

    God Bless the USA

  7. #7
    Join Date
    Sep 2007
    Location
    Somewhere in the world.
    Posts
    1,589
    As stated you should be with someone who understands that piece of equipment who can assist with the troubleshooting and proper diagnostic of the Chiller a YK is a positive pressure machine , also you state its surging is it low side or high side surge all collected readings can assist with proper diagnostic and all Chiller spec's are in sales order screen , and a full M/N & S/N would also help out.
    Arguing with your Boss is like wrestling with a pig in
    mud.
    After a while you realize that while you are getting
    dirty, the pig is actually enjoying it.

    It is not exactly cheating, I prefer to consider it
    creative problem solving.

    25 years ago we had Bob Hope , Steve Jobs , and Johnny Cash today we have no Hope no Jobs and no Cash !
    I can fix broke but i can't fix stupid !

  8. #8
    Join Date
    Jul 2010
    Posts
    6

    level sensor/vane calliberation

    if water side ok on both condensor & evaporator ,make sure small temp diff on condensor with in the limit, & check vane /liquid level sensor & liquid level valve calliberation is ok & its works normally

  9. #9
    Join Date
    Jan 2011
    Location
    North Carolina
    Posts
    20
    The "rumbling" noise that you've stated sounds more like a "stall". Need more info though. Operating conditions? VSD/SSS/EMS? If it is a VSD with VGD(variable geometry diffuser) and there is a light load, it is probably within the previously mapped surge map and the VGD is "probing". With the optivew panel look under compressor/acc detail/surge map, you will probably see the vanes are almost completely shut with the drive slowed to the minimun hz. Just one scenario of many here. Operating log would be the best bet for info here

  10. #10
    Join Date
    Aug 2010
    Location
    hampton roads, Va
    Posts
    16
    agree with klove need to know alot before giving an answer!!!! just as electrical diagrams are like road maps to your destination an approach and log reading will help us help you!!!

  11. #11
    Join Date
    Oct 2010
    Posts
    118
    York 56,aside from operating conditions,and experiance how can you tell the differance between a high head surge and a low load surge? is there a definate differance in sound? and would it be simalar between differant mfg's
    Thanks

  12. #12
    Join Date
    Sep 2007
    Location
    Somewhere in the world.
    Posts
    1,589
    A surge sounds the same what causes it is how you determine which one it is York has a snap shot of the last operating parameters when it faults out you should be able to figure that one out that will tell you which one is the culprite and how to go about fixing the problem.
    Arguing with your Boss is like wrestling with a pig in
    mud.
    After a while you realize that while you are getting
    dirty, the pig is actually enjoying it.

    It is not exactly cheating, I prefer to consider it
    creative problem solving.

    25 years ago we had Bob Hope , Steve Jobs , and Johnny Cash today we have no Hope no Jobs and no Cash !
    I can fix broke but i can't fix stupid !

  13. #13
    Join Date
    Sep 2004
    Location
    Kansas City, Kansas, United States
    Posts
    13,828


    Quote Originally Posted by klove View Post
    You're going to have to get a lot more detailed than what you have. To ask what's causing a surge in a centrifugal chiller without giving a complete operating log is like asking everyone to hunt a needle in a haystack. You do say that design is good. So along with the operating log, it would help if you post the design data on the machine. We also need to know the machine setup.

    You also stated that it wasn't running high head pressure, but if it weren't a 134A machine you'd swear it had air in it. Air in a shell and tube condenser creates a high head condition no matter what type refrigerant you use. I believe it's safe to say that it may be in your best interest to get someone that's familiar with these type chillers to take a look at things.