  1. #1
    Join Date
    Apr 2005
    Posts
    2
    Post Likes
    just installed a goodman AEPT060-001-A-1 WITH A CPLT 48-1 WITH A TH8321U1006 T-STAT. UNIT WORKS GREAT EXCEPT EVERY ONCE IN A WHILE COMPRESSOR IS GOING OUT ON INTERNAL OVERLOAD. PRESSURES ARE EQUALIZING DURING OFF CYCLE. START UP AMPS USUALLY AROUND 35 AMPS EVERY ONCE IN A WHILE AMP DRAW GOES UP TO BETWEEN 95-125 AMPS ON START UP AND THERE IS A LOUD BANG WHEN COMPRESSOR STARTS. ANY IDEAS

  2. #2
    Join Date
    Mar 2004
    Location
    SE Michigan
    Posts
    24,816
    Post Likes
    What are your operating pressures, length of line set, size of line set, TXV or fixed, super heat/subcooling?
    and most importantly, why are you yelling? and is it single or three phase, recip. or scroll?

    [Edited by coolwhip on 04-11-2005 at 12:40 PM]

  3. #3
    Join Date
    Apr 2005
    Posts
    2
    Post Likes
    Thread Starter
    line size is 3/8 head and 7/8 suction line run is 25 ft. scroll compressor, single phase,txv, 13 subcooling ,78# suction,160# head. not yelling just a typo error

  4. #4
    Join Date
    Aug 2003
    Location
    Fort Worth, TX
    Posts
    11,847
    Post Likes
    Originally posted by npr bandit
    START UP AMPS USUALLY AROUND 35 AMPS EVERY ONCE IN A WHILE AMP DRAW GOES UP TO BETWEEN 95-125 AMPS ON START UP AND THERE IS A LOUD BANG WHEN COMPRESSOR STARTS.

    line size is 3/8 head and 7/8 suction line run is 25 ft. scroll compressor, single phase,txv, 13 subcooling ,78# suction,160# head.

    Just going off that little amount of info, it sounds like you may be overcharged and you're slugging liquid back to the compressor. Either that or check your pipe routing and/or consider adding a crankcase heater.
    Psychrometrics: the very foundation of HVAC. A comfort troubleshooter's best friend.

  5. #5
    Join Date
    Mar 2004
    Location
    SE Michigan
    Posts
    24,816
    Post Likes
    May be overcharged.

  6. #6
    Join Date
    Mar 2005
    Location
    Oklahoma City
    Posts
    6
    Post Likes

    Smile

    "line size is 3/8 head and 7/8 suction line run is 25 ft. scroll compressor, single phase,txv, 13 subcooling ,78# suction,160# head. not yelling just a typo error"

    With a TXV metering device you should always have a start booster! The TXV will sometimes cause the compressor to have to start with a high head pressure. Good Luck

  7. #7
    Join Date
    Mar 2003
    Posts
    1,877
    Post Likes
    need subcooling and superheat. sounds like your flooding and
    compressor locking up.

    txv or orfice

  8. #8
    Join Date
    Mar 2005
    Location
    leland nc
    Posts
    4,526
    Post Likes
    i have found some scrolls need hard start
    lenox has a hard start kit for the hs26 and 27 just for this problem. they also recomend it for all units with txv
    also you may be over charged double check subcool and do super heat at the coil to make sure. what is the outside temp and inside temp

  9. #9
    Join Date
    Nov 2000
    Location
    Eastern PA
    Posts
    70,520
    Post Likes
    That TXV is a bleed type that should not require hard start components. My money is on contaminants or partially blocked filter/drier.

    Check the subcooling.
    Training is important!
    Practical Training is a must!

  10. #10
    Join Date
    Nov 2000
    Location
    Eastern PA
    Posts
    70,520
    Post Likes
    Also, check to what speed selection that VS blower is set at. If it was not reset for that heat pump it is running way too high.
    Training is important!
    Practical Training is a must!

  11. #11
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    A little over charged?

    What was teh outdoor temp, and how long was it running when you took your readings.

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •