Results 1 to 11 of 11
    Apr 2005
    just installed a goodman AEPT060-001-A-1 WITH A CPLT 48-1 WITH A TH8321U1006 T-STAT. UNIT WORKS GREAT EXCEPT EVERY ONCE IN A WHILE COMPRESSOR IS GOING OUT ON INTERNAL OVERLOAD. PRESSURES ARE EQUALIZING DURING OFF CYCLE. START UP AMPS USUALLY AROUND 35 AMPS EVERY ONCE IN A WHILE AMP DRAW GOES UP TO BETWEEN 95-125 AMPS ON START UP AND THERE IS A LOUD BANG WHEN COMPRESSOR STARTS. ANY IDEAS
    SE Michigan
    What are your operating pressures, length of line set, size of line set, TXV or fixed, super heat/subcooling?
    and most importantly, why are you yelling? and is it single or three phase, recip. or scroll?
    [Edited by coolwhip on 04-11-2005 at 12:40 PM]
    “Now the freaks are on television, the freaks are in the movies. And it’s no longer the sideshow, it’s the whole show. The colorful circus and the clowns and the elephants, for all intents and purposes, are gone, and we’re dealing only with the freaks.” - Jonathan Winters
    Apr 2005
    line size is 3/8 head and 7/8 suction line run is 25 ft. scroll compressor, single phase,txv, 13 subcooling ,78# suction,160# head. not yelling just a typo error
    Fort Worth, TX
    Just going off that little amount of info, it sounds like you may be overcharged and you're slugging liquid back to the compressor. Either that or check your pipe routing and/or consider adding a crankcase heater.
    Building Physics Rule #2:
    Building Physics Rule #3:
    SE Michigan
    May be overcharged.
    Oklahoma City
    Smile
    "line size is 3/8 head and 7/8 suction line run is 25 ft. scroll compressor, single phase,txv, 13 subcooling ,78# suction,160# head. not yelling just a typo error"
    With a TXV metering device you should always have a start booster! The TXV will sometimes cause the compressor to have to start with a high head pressure. Good Luck
    need subcooling and superheat. sounds like your flooding and
    compressor locking up.
    txv or orfice
    leland nc
    i have found some scrolls need hard start
    lenox has a hard start kit for the hs26 and 27 just for this problem. they also recomend it for all units with txv
    also you may be over charged double check subcool and do super heat at the coil to make sure. what is the outside temp and inside temp
    Nov 2000
    Eastern PA
    That TXV is a bleed type that should not require hard start components. My money is on contaminants or partially blocked filter/drier.
    Check the subcooling.
    ...seek, and ye shall find;..
    Ecclesiastes 10:2 NIV
    Nov 2000
    Eastern PA
    Also, check to what speed selection that VS blower is set at. If it was not reset for that heat pump it is running way too high.
    A little over charged?
    What was teh outdoor temp, and how long was it running when you took your readings.