Results 1 to 13 of 39
Thread: high head?..
    southern illinois
    did a start-up today on furn' chg. out i did a couple months ago...it was 78 out,71 in,i had 300 psi head on this unit....i thought it was kind of high..would a condenser motor that had been changed out have something to do with this..22 super heat and delta t of 20 though?
    Apr 2003
    the Great Pacific Northwest
    Condenser motor change. Absolutely, I'll bet the condenser air discharge was unusally hat also.
    Its possible, check if its the right rotation.
    Is there any chance you put a kink in the line while changing the furnace.
    What was the suction pressue.
    southern illinois
    67-68psi..discharge temp was 122, liq. line temp of 115...
    Houston,Tx.
    You never opened up the system? if you did not the system probably has been running these pressures before you touched it. What was the suction? if it was normal, the condenser may need a good bath, or check temp. on each side of the liquid drier. Just some thoughts.
    southern illinois
    condenser was not plugged or anything....
    West TN
    Guess its that time of year again to dust off the old
    air conditioning brain cells.
    http://www.hvac-talk.com/vbb/showthr...threadid=55974
    Extend to others the grace that God has given you.
    southern illinois
    no dryer,no kinks,and i recovered refrig. took out coil cleaned it and pulled vacum recharge new refrig....by the way this is cap-tube coil..
    Houston,Tx.
    O I hate it when that happens
    Any cap tubes freezing up? what was the suction pressure?
    and the furnace is geared for the right amount of cfm's for the evap. coil? was it very humid inside the house when you started the system? this can cause a higher than normal head until some of the humidity is removed.
    leland nc
    you sure you didnt over charge the system
    some of the old cap tube coils ran low back arround 55 to 60. if the blower is not putting out enough cfms it will be lower. very easy to over charge a cap tube since we are used to today coils with 70 to 90 lb back
    Apr 2005
    Ms.
    clean the od coil. picking up heat may not be getting rid of it.
    Houston,Tx.
    I have run across them that looked pretty from the outside then I got out the water hose and it looked like a mud slide on the slab.
    Houston,Tx.
    This is true! Tin, we are telling our age.