    Tewksbury
    what formulas are used to charge water source heat pump by pressures?
    if metering devise is txv use subcooling if orfice use charging chart and superheat
    Feb 2005
    small island in the Pacific Ocean
    why do you need to charge it. geo units come charged and all you do is hook up the water
    Dec 2001
    you dont charge wshp's by pressures you weigh the charfe in!!!!!
    Allen
    try this link from a while back
    http://www.hvac-talk.com/vbb/showthr...threadid=69615
    [Edited by acddc on 04-10-2005 at 02:48 AM]
    North Florida/South Georgia
    Talking allow me to weigh in on this one
    Weight.
    All my leon freaked out!
    Apr 2005
    where the beer flows like wine
    weight the charge and add a few extra ounces to compensate for the refrigerant trapped in your hoses, those units are very anal about their charge, every time you hook your gauges to one of them,fill you hoses with refrigerant before you do it.